Upgrading an old SLC line to CLX / safety

I'm quoting a big line upgrade that currently has a L55 and 7 SLC 5/01 processors, all of which are islands. I plan to change to an L71S and my original intention was to use PointIO in the SLC cabinets (there are only 3-4 modules in each cabinet) and to use Guard IO so it can all be controlled from the GuardLogix. However, all the IO in the remote cabinets is 120vac and it doesn't look like there are any 120vac Guard IO modules, so I'm considering the 440C Guardmaster in conjunction with the regular PointIO modules. Replacing all of the existing motor starters with 24vdc coils is out of the budget for this job.
Does anyone have another suggestions that I'm not seeing?
  Reply With Quote
Old October 17th, 2017, 08:04 AM   #2
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,234
Use terminal mounted isolation relays. I do that almost all of the time for outputs (24 VDC Driver for 120 VAC output), and sometimes for inputs. No reason you can't.
__________________
------------------------------------
How to ask questions the SMART Way!

Look First, Ask Second!

  Reply With Quote
Old October 17th, 2017, 10:27 AM   #3
phuz
Member
United States

phuz is offline
 
Join Date: Jun 2008
Location: Mohnton, PA
Posts: 744
Quote:
Originally Posted by rdrast View Post
Use terminal mounted isolation relays. I do that almost all of the time for outputs (24 VDC Driver for 120 VAC output), and sometimes for inputs. No reason you can't.
And that will meet safety requirements?
  Reply With Quote
Old October 17th, 2017, 11:07 AM   #4
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,403
Quote:
Originally Posted by phuz View Post
And that will meet safety requirements?
Sure. If you use safety relays: http://ab.rockwellautomation.com/Rel...Control-Relays
__________________
  Reply With Quote
Old October 17th, 2017, 11:24 AM   #5
phuz
Member
United States

phuz is offline
 
Join Date: Jun 2008
Location: Mohnton, PA
Posts: 744
Quote:
Originally Posted by Bit_Bucket_07 View Post
Good enough for me! Thanks.
  Reply With Quote
Old October 17th, 2017, 01:07 PM   #6
kolyur
Lifetime Supporting Member + Moderator
United States

kolyur is offline
 
kolyur's Avatar
 
Join Date: Oct 2004
Location: Wooster, Ohio
Posts: 1,403
Keep in mind that in order for force-guided relays (aka "safety relays") to be effective, the normally closed auxiliary contact needs to be used as an EDM circuit back to the controlling safety device. There is nothing special about these relays except that the contacts are mechanically linked so you can detect a welded contact by monitoring the NC pole. If this is not done then the safety relay offers no advantage over a general purpose relay.
__________________
John
  Reply With Quote
Old October 17th, 2017, 01:14 PM   #7
phuz
Member
United States

phuz is offline
 
Join Date: Jun 2008
Location: Mohnton, PA
Posts: 744
Quote:
Originally Posted by kolyur View Post
Keep in mind that in order for force-guided relays (aka "safety relays") to be effective, the normally closed auxiliary contact needs to be used as an EDM circuit back to the controlling safety device. There is nothing special about these relays except that the contacts are mechanically linked so you can detect a welded contact by monitoring the NC pole. If this is not done then the safety relay offers no advantage over a general purpose relay.
Makes perfect sense. Thanks.
  Reply With Quote
Old October 17th, 2017, 01:24 PM   #8
mellis
Member
United States

mellis is offline
 
Join Date: Nov 2004
Location: Cincinnati, Ohio
Posts: 802
Quote:
Originally Posted by phuz View Post
And that will meet safety requirements?
It is hard to say.

We don't have any data on your safety requirements.

My initial thought is if you are replacing SLC5/01 I/O then your requirements aren't very high. Likewise if the motors starters do not include safety contactors, then safety relays to pull in the contactors are probably not needed either.

However, if you intend to raise the level of safety required in this upgrade, you will need to evaluate how you will meet those requirements.

You can't just throw "safety" hardware at everything and it will be ok.
  Reply With Quote
Old October 17th, 2017, 01:30 PM   #9
phuz
Member
United States

phuz is offline
 
Join Date: Jun 2008
Location: Mohnton, PA
Posts: 744
Quote:
Originally Posted by mellis View Post
It is hard to say.

We don't have any data on your safety requirements.

My initial thought is if you are replacing SLC5/01 I/O then your requirements aren't very high. Likewise if the motors starters do not include safety contactors, then safety relays to pull in the contactors are probably not needed either.

However, if you intend to raise the level of safety required in this upgrade, you will need to evaluate how you will meet those requirements.

You can't just throw "safety" hardware at everything and it will be ok.
I knew this reply would come . I was referring to safety levels along the lines of GuardLogix and Guard I/O control. The previous responses were just what I needed. Safety relay with monitoring feedback is perfect. The existing system, I believe, uses standard relays to drop out the starters. They currently have a keyed bypass switch to bypass numerous safety components, so this is a much needed upgrade.

On another note, is there a reason they have limited Guard I/O modules? I am still surprised that there are no 1756 modules.
  Reply With Quote
Old October 17th, 2017, 06:54 PM   #10
Timbert
Member
United States

Timbert is offline
 
Timbert's Avatar
 
Join Date: May 2011
Location: The middle of the Pacific Ocean
Posts: 368
Quote:
Originally Posted by phuz View Post
Safety relay with monitoring feedback is perfect. The existing system, I believe, uses standard relays to drop out the starters. They currently have a keyed bypass switch to bypass numerous safety components, so this is a much needed upgrade.
I might be misunderstanding but it sounds like you are planning on using force-guided relays to control the existing starters which act as your final disconnecting means. Assuming your using Guardlogix because you need to meet SIL 3 (ControlLogix can support up to SIL 2). Unless the existing starters have force-guided contacts I doubt that you will be able to meet your safety requirements as you must have feedback from your interposing relay as well as the final output contactor.
__________________
An expert is a man who has made all the mistakes which can be made in a very narrow field. --Niels Bohr as quoted by Edward Teller
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SLC to CLX, and other questions the_msp LIVE PLC Questions And Answers 2 May 12th, 2015 01:37 PM
Message SLC 505 to SLC 504 via DHRIO lenny1587 LIVE PLC Questions And Answers 2 April 9th, 2015 02:47 PM
CLX to SLC Messaging-Source Format ?? scottmurphy LIVE PLC Questions And Answers 4 April 28th, 2009 04:08 PM
Safety category assessment for an assembly line. hjcl LIVE PLC Questions And Answers 8 April 8th, 2007 09:08 PM
SLC vs CLX smiller LIVE PLC Questions And Answers 11 September 10th, 2004 06:30 AM


All times are GMT -5. The time now is 03:33 AM.


.