Modbus communication.

rejoe.koshy

Member
Join Date
Dec 2011
Location
kolkata
Posts
195
Hey guys ,
I am in a bit of confusion regarding modbus communication.I have MLX 1200 which uses its channel 0 port as a "RTU master" and is connected to a 1761-net AIC module at (8 pin RS 232 port), it then uses its RS485 port to communicate with drives.

Next I have a MLX 1400 controller , which also is configured as RTU master but doesnt use a NET AIC module to communicate with devices on RS 485 network.

As per my understanding NET AIC module is used to convert a RS232 signal to RS485 , if so then how come MLX 1400 is able to communicate without NET AIC??, where as both controllers are configured as RTU master..

Pls help
 
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1762-um001_-en-p.pdf
"The MicroLogix 1200 can be connected to a personal computer. It can also be
connected to a DH-485 network, or a Modbus network as an RTU Master or
RTU Slave using an Advanced Interface Converter (catalog number
1761-NET-AIC)."

https://ab.rockwellautomation.com/Programmable-Controllers/MicroLogix-1400
"Two serial ports with DF1, DH-485, Modbus RTU, DNP3 and ASCII protocol support"

The 1400 has built in protocol support for Modbus RTU, 1200 needs the 1761-net AIC module for Modbus RTU protocol support.

Regards,
 

Similar Topics

Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
51
Hi all I need help on this As in my project used Schneider TM241 controller. Now I want to communicate Elite energy meter with controller by...
Replies
3
Views
116
Hello, I need to access the bits from the fire system control panel through RS-485. So, I used Read Var block to read from the panel...
Replies
0
Views
170
Hi, i cant establish communication between fatek plc with an energy meter, both capable for modbus tcp, i did with modscan but fatek plc does not...
Replies
1
Views
142
Hi Guys, I am a new member and this is my first post! I have a little PLC experience but it is mostly with siemens logo and using ladder...
Replies
4
Views
893
Back
Top Bottom