TIA V15 and Lenze Drives

thiseful

Member
Join Date
Oct 2017
Location
Germany
Posts
19
Hello ladies and gentelmen

I am working on a project with TIA V15 and Lenze drives (8400 motec, 8400 protec, 9400 HL ...) and I must use the device tool for Lenze : EasyStarter.


I received some configuration files for the drives , with the termination .LPK .Ddo you have any idea how may I upload the parameters in the drives using .lpk files and EasyStarter?

P.S I could not find some proper documentation regarding EasyStarter.
 
Meanwhile I found the solution:

Using Easy Package Manager install the packages (.lpk files)
Then using Easy Starter ( Application Loader) extract the application from the installed package and download it to the device
 