Why are Internet Protocol settings unavailable (grayed out) in Compactlogix L24 controller properties? None of the IP settings have been configured yet the controller communicates properly.

Gracias
 
If the Controller is set to get a dynamic IP(Bootp or DHCP) the other settings will be greyed out.
Set it to use a static IP and you may change these.
 
Why are Internet Protocol settings unavailable (grayed out) in Compactlogix L24 controller properties? None of the IP settings have been configured yet the controller communicates properly.

Gracias

These values are not available when you are offline. CompactLogix processors network address is not saved or configured in the offline file like with Logix500 based processors. To change the IP address you need to connect to the processor using the USB (or serial on older models) and change it via RSLinx, or use the BootP protocol.
 

Similar Topics

Hi everyone, i have a compact logic 1769-L18 PLC and I'm using FTalk View ME for the display. I wanted to do some visualization on Grafana. At...
Replies
1
Views
95
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
95
Does this instruction calculate values during a single scan, or does it require number of scans based on element count in the array? For Example...
Replies
3
Views
112
Hello all, and thank you in advance for any assistance you may be able to provide! This is my first post, so if I need to reformat or change...
Replies
8
Views
467
We are trying to poll data coming from a PLC for remote monitoring we have the IP address of the PLC and the default port number and the path is...
Replies
25
Views
568
Back
Top Bottom