Communication Issue

galaxian11

Member
Join Date
Nov 2014
Location
Ohio
Posts
16
I am having problem with communication between a Compactlogix 5380 using version 30 and a Panelview Plus 6, 700 version 6.1. I have the PLC Ethernet/IP
mode set to A1/A2:Linear/DLR...PLC and HMI connected to N-Tron switch. The PLC IP is 192.168.1.100 and HMI 192.168.1.101. I can download to both from my PC, but the PLC and HMI do not communicate. Can someone please help me? Thank you...
 
Is your shortcut setup correctly? Make sure you're pointing your shortcut to the PLC. Make sure your pages work when you press the play button in FTVME. If it is working like it should, copy the shortcut to the runtime tab. When you download, make sure you Replace Communications.

Good Luck.
 
Technote #1030822 indicates you need FW 9.0 for your Panelview to correctly support V30 FW for Control and CompactLogix.

Now, I've had the same problem before w/ a PVP 6.1 FW and talking to a L7x processor, which I solved by manually changing the runtime device from a L7x to a L6x processor. You *might* be able to accomplish the same thing by changing to an older compactlogix in your shortcut.
 
On a different note, I’d change the IP addresses away from “192.168.1.xxx”. That is by far the most common address scheme out there if for no other reason than it is the default in about 80% of the Ethernet equipment sold (usually 192.168.1.1). .100 is also a very common fourth octet so you’re opening yourself up for hacking.
 
Yes...all the subnet masks are the same. Also...the shortcut seems to be set up correctly. I can test the app and it works fine. I tried creating another runtime application, then selected the "Replace Comms" before I downloaded, but still no luck. I will try Dravik's solution since I am also using a PV with FW 6.1 and Compactlogix FW30.

Thanks so far for everyone's input!!
 
OK...I finally got a chance to get back here and post the outcome of my issue.
I found out that Dravik was almost correct in that I needed a later FW version for the Panelview to support the FW version 30 Compactlogix. My Panelview Plus needed at least FW version 8.2.

Thanks everyone for the support!!
 

Similar Topics

Currently,we are facing the communication go through with 422 tx+ and tx-. Mitsubishi fx5u series is used and using command rs2. But the package...
Replies
0
Views
100
Hello, a customer i support has DH+ RIO racks all over the plant. they use 1794-asb modules. today they had a rack fault out and go unresponsive...
Replies
0
Views
643
Hi Everyone, We went through a tough time that Power flex-250KW Drive Thyristor burn out and MCCB tripped at feeder side, but in SCADA VFD was...
Replies
3
Views
789
Hi, I'm trying to set up a new VFD to our profi network and I can't get it connected to the PB3 REM module. I chose (352) Siemens telegram 352...
Replies
10
Views
1,741
Hey Guys, I am struggling to read data from a "JUMO" make controller using modbus RTU with MLX1400. The communication between the devices has...
Replies
18
Views
5,068
Back
Top Bottom