Help required For Guard Logix CPU L71S

We are facing following problems for gurad logix

1) How we can edit the safety Program and safety tags

2)Could not change the Safety Modules Properties

Is there is any procedure for that or it is software end Problem using Studio 5000 standard edtition

After that we send Empty program with Existing Hard ware then At online it gives I/O Not OK communication not established bw EN2tr to AENTR and its safety point ios
 
You have to unlock the safety to change anything safety related....in the upper left of logix while online does it show locked or unlocked?
 
You can't modify any safety programs using Logix Standard Edition. You will need Full or Professional edition.

And, as robertmee said, you'll have to have the safety unlock password too.
 

Similar Topics

Hello, I'm adding an Allen-Bradley SensaGuard door switch (440N-Z21SS2H) to a small existing machine to drop out pneumatic function when the...
Replies
3
Views
842
Hi to the forum. I have a logic problem which is confusing me. From my sketch I have seven conveyors that I control using a twido PLC via canbus...
Replies
19
Views
5,573
Hi!! I'm looking for Temperature rise calculation software from Rockwell, I just download "Product selection toolbox 2022" but this software is...
Replies
1
Views
111
Please see attached file. I need this program in Function Block form but I am totally lost on this. Any help would be appreciated. Thanks!
Replies
8
Views
260
Took a new job and the controls schemes are fairly old and I'm used to Allen Bradley and Siemens. I'm looking to replace a pair of Superior...
Replies
1
Views
85
Back
Top Bottom