5069 serial - Write problem, Read is OK

TheWaterboy

Lifetime Supporting Member + Moderator
Join Date
May 2006
Location
-27.9679796,153.419016
Posts
1,924
I am starting up a new RTU using a L306ER with a 5069 -serial to a Serial radio using DF1 Radio Modem Protocol. I only used it for reading to get the station set up and READS work fine. then I wanted to write... and no.
I was on the phone with Rockwell for 2 hours today and they couldn't make it work either.

I know there were a couple folks that tested this module when it got that firmware update that enabled DF1, but is anyone using it for real and had this work?

Equipment involved is a L81 processor, which is using an adjacent L61 processor as a serial port, then to the Radio pair and then to the RTU with the 5069-serial.

I have mapped the data table in the remote RTU and that mapping works for a read MSG but Writes result in a 16#001f extended _0204.

Anyone else seen this?

Oh and I use this same setup already with 3 ML1400's in RTUs and those work fine so the hardware is sound, the difference is the L306er and the serial module .
 
Last edited:
For those playing the home version of this game.. the Write MSG was created as "Connected" and that just wont work.
It's greyed out once the MSG is created you can't change it. You have to create a New MSG and not have that box checked. Must have fat fingered it.
 

Similar Topics

I have a new L306 CompactLogix running V33 with a 5069-Serial module in order to send data through RS-232 to a Sato S84EX printer. I'm unable to...
Replies
1
Views
1,327
Does any one have a copy or a source for the v2.012 AOP for the 5069-Serial. If I go to the product compatibility and download center for...
Replies
2
Views
1,434
Hello friends. Old PLC: SLC 5/05 1747-L552 connected to a Dataradio T96SR radio. New migrated PLC: 5069-L330ER with a 5069-SERIAL module. FW...
Replies
8
Views
3,153
Hi all! I'm using a 5069-SERIAL card for the first time, though I have plenty of experience with serial on other AB platforms. I'm running into...
Replies
9
Views
3,798
Hi, Our L306ERS2 PLC controls a 5069-SERIAL A FW 1.011 programmed with Studio 5000 V32.11. When receiving data the module's diagnostic shows the...
Replies
4
Views
2,192
Back
Top Bottom