Hi there pals, i have a problem, i am working in a project with Ifix, i have to command some valves in a line from Chile to Argentina. The think is.. we cannot move the valves with the Ifix, i know the problem is just Ifix cause we moved the valves forcing the bits of the PLC with Modscan and the valves did the operation, we also know the command we are sending to open and close the valve is ok from the Ifix Workspace, the database and the MBE.. we can observe them in these points, so in one point from the MBE to the PLC we have a problem.... we also know the adresses we are pointing are ok, cause are the same adresses that we pointed with the Modscan and did the operations... if any one can help me with this, that'd be great!

PS: Sorry for my english, this is not my native language, i hope you can understand me.
 
I read as you can't change a PLC value with iFix.

-Which PLC?
-What's the HMI driver? OPC?
-What iFix block are you using?
-How is Modscan figure in all this?

maybe a diagram would help.
 
Need more info but a couple things to start

The DI Tag in the iFi database might not have Output Enabled checked.

Add @BOOL to the end of the tag address
 
hi pals! we solved it, but i am corious about what happened.

the plcs were old Modicon 984 series.
the things is ... we can now control the valve with the open / close commands, in mbe we had to create an unsigned integer variable for the all register where the bits of open and close command have to be writen. we have to write the integer equivalent of the boolean values ​​and the valves open and close ok now ... idk why the bools didn't work, but this other way actually works ok.
when i return to the plant i will try to check deeper why the boolean way didn't work.
 

Similar Topics

Dear all, I am beginer in ifix hmi programming. I have 2 ifix 6.0 pc with license FiX and client.. Can some one tell me how to configure sample...
Replies
0
Views
139
Hello, I have to deal with iFix again and am looking at the most efficient way to create alarms to display in iFix, i.e. not creating an...
Replies
0
Views
149
Hi everyone. I'm beginner with Ifix. I'm appreciate if you share me some document to understand how to play with Ifix 6.0. By the way, I have some...
Replies
11
Views
687
Hi everyone. Ifix scada is new for me. Please help help me to clarify is it possible to open Ifix scada runtime on dual monitor and how to do? Thanks
Replies
1
Views
436
Hi team! I'm starting some iFIX application migrations and some of them are being developed with the high performance library. Some objects that...
Replies
4
Views
807
Back
Top Bottom