Good Afternoon ,

I am working on a project on the desk , and I am getting DC Bus Voltage , Current , and Fault Codes from my PowerFlex 525 to my CompactLogix. The only fault I have gotten from the drive , during commisioning , is 73 ( F073 EN Net Loss) . I am able to clear the actual drive fault , from my HMI , using the Clear Fault tag to the drive , but the Fault 73 ( F073 EN Net Loss) is still present from the drive. I tried to type a 0 in it to override it , but it refered back to 73. I have this on all 3 drives. What could be causing this ?

Thanks so much in advance ,
 
That datalink will give you the last recorded fault - not the present fault. It's "fault 1 in the history", not "number one fault".

There's no way to stop it reporting that value - typically what I do here is map it all into an AOI, then have an output DINT tag called "FaultCode" which I set to zero if the drive is healthy, and if I get a "fault" signal from the drive I move the "Fault 1 Code" from the drive into the AOI's "FaultCode" output.

[edit] It's actually pretty useful to have that value hang around, because even if operators reset the fault and keep going, you can look and see what it was after the event
 
Thanks for the advice ,

So the Fault Code that I am seeing will be overwritten by a new fault , correct ? So for example , 73 ( F073 ) will stay around , until another fault such as F005 ( OverVoltage ) , overwrites it , correct ?

Also , I would like to display Freq.Drive alarm details on the HMI. I took notice that the alsrms are , for example F002 to F127. My question is , how will the fault code , from the drive , display . 002 or 2 ? I would like to use a Multistate Indicator so that I can display detail , and troubleshooting tips on the HMI.

Thanks Again ,
 
Correct, that fault code is the top fault in the queue, so if any other fault occurs, the new fault bumps the previous one down the list and the new fault code shows up in FaultCode1.

The fault code is an integer. So fault code F002 will literally be transmitted as "0000_0000_0000_0010" which, if you choose to view it as an integer, will be "2".
 

Similar Topics

Good Morning , I'm working on a project that I may need to change the acceleration rate according to which recipe is being ran. I took notice...
Replies
2
Views
2,194
Good Morning , We have been running a machine , PLC and PowerFlex 525 for over a year. For some unknown reason , I have a Yellow Triangle on...
Replies
9
Views
4,423
Good Morning , I am working on a project with some PowerFlex 525 drives. I am using CompactLogix 1769-L18. I took notice that the tags that...
Replies
23
Views
22,477
PowerFlex 525 - can you access the parameters from a MicroLogix 1400 & CompactLogix Good Morning , I have a separate stand alone machine...
Replies
2
Views
3,333
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
213
Back
Top Bottom