PLC - outputs emitting current when not energized?

Hi all,

I come to the forum for a strange encounter with some LED indicators I bought for a project. The LEDs were cheap ones from China, $5 for a 3 pack of yellow, green, and red. Not sure if they are "true" LEDs or not, but they do say LED on the back, with some Chinese writing in addition.

The problem I am experiencing is that the LEDs are receiving some power when connected to the PLC outputs because they light up faintly. When I first wired it up, turned the PLC on, i figured the output were energized from a recent program I wrote to the controller. Well, thats not the case. I cleared the memory from the PLC and wrote an additional program to actually energize the LED outputs. Then they get full brightness.

So it's obvious the LEDs are receiving some current, I just don't quite understand why that is. If anyone could help me out to understanding why they have a dim light when the outputs aren't energized, that would be great.

Heres some more information:

1. This occurs even when the PLC is not powered up.

2. This occurs regardless of switching terminals on the LED

3. A single LED has simply two terminals.

4. The PLC is a CLICK and the LEDs are connected via an additional 120VAC-240VAC discrete relay output module

5. All input and output devices are 120VAC and the PLC is powered with a 24VDC CLICK PSU.

6. All commons are wired to the CPU and the additional output module

7. The LED(s) is wired from HOT120VAC to one terminal, and then out directly to the output module.




Thanks in advance!

Last edited by bmillerx94; March 20th, 2017 at 09:33 PM.
  Reply With Quote
Old March 20th, 2017, 10:34 PM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,411
Quote:
Originally Posted by bmillerx94 View Post
4. The PLC is a CLICK and the LEDs are connected via an additional 120VAC-240VAC discrete relay output module

---

7. The LED(s) is wired from HOT120VAC to one terminal, and then out directly to the output module.
I was going to rush to tell you all about leakage current with solid state PLC outputs, but then you said the outputs are relays. So I am focussed on that last statement.

How are they wired? Are the LED lamps rated for 120VAC?
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old March 20th, 2017, 10:38 PM   #3
bmillerx94
Member
United States

bmillerx94 is offline
 
Join Date: Feb 2017
Location: United States
Posts: 26
Okie,

The LEDs are rated for 120VAC. One side is connected to 120VAC hot, the other side to the PLC output.

I didn't mean to confuse about relays. I simply said "relay outputs" because that is what the actual module is called. They are not connected to relays.

So it must be this leakage current. Is this preventable internally with some.settings or is additional hardware required?

Thanks
  Reply With Quote
Old March 20th, 2017, 10:41 PM   #4
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,411
I would normally wire 120vac to one side of the controlling relay (even if it is a PLC relay) and out of that relay normally open contact to one terminal of the lamp, and the other terminal of the lamp to neutral.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old March 20th, 2017, 10:47 PM   #5
bmillerx94
Member
United States

bmillerx94 is offline
 
Join Date: Feb 2017
Location: United States
Posts: 26
OkiePC,

Hmmm. So I would basically wire 120vac hot into the output terminal for the LED output, then out of that same terminal, run a wire to the LEDs first terminal. Then the second terminal back to common?
  Reply With Quote
Old March 20th, 2017, 10:49 PM   #6
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 3,607
I think OkiePC understood what you meant; that the output module is a relay output module.

If you look at this pdf:

https://cdn.automationdirect.com/sta...cs/c004trs.pdf

it shows varistors between the internal contacts and common. I suspect you are getting some small amount of leakage through these varistors; enough to faintly light the LEDs. It doesn't look like this can be disconnected. A burden resistor might help with this but I've never tried to use those with an LED.

Keith
  Reply With Quote
Old March 20th, 2017, 10:56 PM   #7
bmillerx94
Member
United States

bmillerx94 is offline
 
Join Date: Feb 2017
Location: United States
Posts: 26
Keith,

Thanks for clearing up any unintentional confusion. I did see that schematic before, but I never really knew what a varistor was so I didn't catch that. So, I'm learning, that's good.

So, would this leakage current be a result of using a variable voltage output module? Since it supports 120VAC - 240VAC, I suspect this is a reason? Perhaps if I wired the LEDs to output on the CPU itself, which only supports 120VAC if I am correct, then maybe this would behave as I want it to.

Thanks
  Reply With Quote
Old March 20th, 2017, 11:09 PM   #8
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 3,607
Which module are you using exactly? If it is a relay module there is a much broader range than 120-240.

It isn't the voltage range that is the issue. It is the solid state component across the contacts. Check this if you haven't:

https://en.wikipedia.org/wiki/Varistor

Varistors are put across the relay contacts to help suppress voltage spikes due to inductive kickback from coils that might be controlled by the contacts. These spikes can cause arcing between the contacts as they open, shortening the life of the contacts.

One thing you might try to do is put a true relay in the circuit. Control the relay with a plc output and control the LED with contacts from the relay. None of the freestanding relays I am familiar with have surge suppression built in across the contacts.

Keith
  Reply With Quote
Old March 20th, 2017, 11:15 PM   #9
bmillerx94
Member
United States

bmillerx94 is offline
 
Join Date: Feb 2017
Location: United States
Posts: 26
Keith,

It turns out it is not a relay output module, at least is not listed as that from what I see. I was also incorrect about the voltage range, which is actually 17-240. The model can be seen here:

https://www.automationdirect.com/adc...utputs/C0-08TA

Great explanation on the varistors. That makes sense. I may have to purchase a relay and give it a go.

Thanks
  Reply With Quote
Old March 21st, 2017, 12:24 AM   #10
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,411
Aha! Triac Leakage. My first suspect...

http://www.plctalk.net/qanda/whereis...=triac+leakage
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old March 26th, 2017, 08:32 AM   #11
shooter
Member
Netherlands

shooter is offline
 
shooter's Avatar
 
Join Date: Sep 2002
Location: duketown
Posts: 2,601
any output leaks a little, or by type (triac) or by snubber circuit .
Even a relays has this snubber so a led will light up at 2 mA.
A simple way to solve it is by adding resistors over the leds, to have the stray diverted to the resistor.
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC outputs on and shouldn't be sparkie LIVE PLC Questions And Answers 11 August 9th, 2015 09:55 AM
PLC outputs updating kallileo LIVE PLC Questions And Answers 2 October 22nd, 2013 11:09 AM
PLC output to solenoid valve. colehan LIVE PLC Questions And Answers 1 August 12th, 2013 03:27 PM
Control current using a PLC PaulKraemer LIVE PLC Questions And Answers 1 November 14th, 2008 03:26 PM
Hard wiring the PLC Doug Hylton LIVE PLC Questions And Answers 46 October 23rd, 2007 12:21 PM


All times are GMT -5. The time now is 09:28 PM.


.