No device is responding as the online active keeper on this network
hammed
Mar 2017
Ibadan
Hello everyone.
Please I need help with configuration on my rsnetworx for controlnet. I get a message that says "No device is responding as the online active keeper on this network" when I try to download to network on the rsnetworx for controlnet.
Any help will be appreciated.
Hello everyone.
The online active keeper should be the lowest address - in this case, address 1
If it is not the active keeper (since it has no config, or whatever) you have a problem. Try removing the Controlnet card from the rack, or just disconnecting the coax from it. If address 2 has a valid config you should be able to download. When all is good, you can add address 1 back in and ... if I remember correctly .. the same config in all of the other controlnet nodes will trigger node 1 to copy the running config of the next address up (2,3,4, whatever)
It`s been a while since I`ve configured a controlnet without a valid keeper ... so if this does not work, post again.
Been a while since I changed anything on a Controlnet, but as I recall "Scheduling" went something like this:
-PLCs should have required I/O configuration
-All devices should have node numbers configured, be powered up, and connected to network
-All controllers that use the network need to be in program mode.
Open up RSNetworx for Controlnet
Browse and go online to the desired network.
Go file-save which will prompt you to "schedule" the network. Say yes.
Put your processors back to run mode.
Hello. After installing the latest Codesys V3.5 SP17 Pach 1, Win V3 x64, on some of our Windows 10 workstations it is impossible to load a program...
3,088
Hello guys! I have a problem with reading tags from S7-300 with 343 module. I checked siemens communication settings hundred times with kepserver...
5,020
Hi I am tryin to use the OPC Quick Client, however I am receiving the following error: Siemens S7-200 Device 'Channel1.Device1' is not...
2,862
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
54
Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
111