Siemens IB to QB transfers
In Siemens s7-300 are IB and QB calls internal bytes or would QB17 overwrite Q17.0 through Q17.7 ect?
Old September 10th, 2019, 01:45 PM   #2
mk42
United States
mk42 is offline
QB17 would overwrite Q17.0 through Q17.7.
Similarly, QD16 would overwrite QB16-QB19 (which would be Q16.0-Q19.7 or QW16-QW18).
Old September 10th, 2019, 01:51 PM   #3
bdb1324
United States
bdb1324 is offline
Thank you that clears up a lot for me. So another example B#16#3F is in hex when it gets transferred to QB17 will it be in binary form or decimal or hex?
Old September 10th, 2019, 02:28 PM   #4
mk42
United States
mk42 is offline
Bin vs Hex vs Dec is just how you view the number. It's all the same to the PLC. You pick how you view it, just like you can in the windows calculator.
Old September 10th, 2019, 03:35 PM   #5
bdb1324
United States
bdb1324 is offline
I guess what I meant was will it store it as
qb17 0 0 0 0 0 0 0 3F
qb17 0 0 0 0 0 0 0 63
qb17 0 0 1 1 1 1 1 1
Old September 10th, 2019, 04:01 PM   #6
mk42
United States
mk42 is offline
Let me ask a question then. What do you think Q17.0 represents?
Old September 10th, 2019, 11:24 PM   #7
sigmadelta
Canada
sigmadelta is offline
qb17 B#16#3F
qb17 63
qb17 2#0011_1111
Yes. Think of it like representing 1 meter = 100 cm = 1000 mm.
__________________
Automation Programmer
PLC / HMI / SCADA / SQL
New Systems, Modifications
System Upgrades & Conversions
Visit: contrologica.com
Email: info@contrologica.com
Old September 10th, 2019, 11:48 PM   #8
sigmadelta
Canada
Like mk42 said, in Windows Calculator:
63 DEC = 3F HEX = 0011 1111 BIN
They are all the same value represented in different numbering systems.
__________________
Old September 11th, 2019, 04:40 AM   #9
parky
United Kingdom
parky is offline
parky's Avatar
I am perplexed by this QB is the same. i.e. Bit Q 0.0 is the first bit of QB0 so why would you transfer it, on the other hand transferring a IB to QB will overwrite the QB with the exact data in IB. If you are talking about I/O refresh then PIB (the actual real Input Image) transferred to IB will update the internal image at that period in time, The real input image is transferred to the internal image outside the normal scan of the code (Dependant on type of PLC) i.e. Before or after code scan the input/output image is updated. If the program scan is 100ms then the Images will be updated every 100ms, however calling a block that updates the I/O image (L PIB 10 T IB 10) will update it immediately, There can be various ways to update, Calling the update function in an interrupt or by calling the FB many times in OB1 between calls to other blocks. Calling it in interrupt will update either in I/O interrupt (update when real inputs change) or if say scan of PLC is 100ms calling the block many times in OB1 will update in the following manner
OB1 total scan of PLC 100ms
JU PB X (5ms)
JU FB Update
JU PB y (10ms)
JU FB Update
JU PB Z (15ms)
JU FB Update
Would update the image after 5ms, 10ms & 15ms etc.
Old September 11th, 2019, 06:31 AM   #10
sigmadelta
Canada
IB and QB are not internal bytes - MB are internal bytes. QB 17 consists of Q17.7 to Q17.0 (most significant bit to least significant bit). 8 bits = 1 byte
IB is Process Image Input Byte
QB is Process Image Output Byte
PIB is Peripheral Input Byte
PQB is Peripheral Output Byte
The scan sequence for the S7-300 (with MMCs) is as follows (simplified for this thread):
Write to Process Image Outputs
Read from Process Image Inputs
Execute Code (OB1 & any other OBs for interrupts, timed interrupts, etc.)
Repeat
Peripheral Inputs and Peripheral Outputs are immediately read from and written to the physical I/O at the very spot in the program where they are encountered.
Process Image Inputs and Process Image Outputs are read from and written to the physical I/O at the beginning of the scan.
There isn't really anything more to it than that... other than you can have multiple Process Images in some CPUs, but that's a bit more advanced than the question of this thread.
__________________
Old September 11th, 2019, 11:10 AM   #11
bdb1324
United States
bdb1324 is offline
Thanks everyone for the comments that was a huge help. The program calls FC41 to measure the width of a plate for blasting and painting. Once that is done the program uses a transfer from IB9 to QB17 if the plate is between a certain width if not the program transfers B#16#3F to QB17. Reason for the questions.
FC41 only gets called when the plate is at a certain position on the conveyor.
Thanks for all the information. They are transferring it to an Allen Bradley PLC and I am trying to understand what the Siemens PLC was doing. So very much appreciated.
Old September 12th, 2019, 08:38 AM   #12
parky
United Kingdom
parky is offline
parky's Avatar
According to Siemens FC41 is a communication block (FTP) as standard, however it can be changed to another FC number, If it is the original then there must be some communications going on. FC 41 is also reported to be a PID (which if I remember correctly I have used). If you can open it, it may be that it is one created by the programmer. It seems a bit confusing to me. It sounds like they are not using interrupts for counting purposes (unless it is done elsewhere) but are transferring the data to outputs like some parallel interface i.e. a value that represents the size.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Siemens or Omron? Gromit LIVE PLC Questions And Answers 35 November 14th, 2017 10:44 AM
AdvancedHMI - Siemens PLCs S7-200/1200/300/400 Beta drivers BryanG LIVE PLC Questions And Answers 25 December 3rd, 2013 03:21 AM
Siemens to Allen Bradley sweetjohnny LIVE PLC Questions And Answers 4 April 20th, 2013 02:46 AM
Siemens 505 to Siemens S7 Rob S. LIVE PLC Questions And Answers 5 July 10th, 2012 08:37 PM
Transfer Data From Siemens PLC to AB PLC Danocane LIVE PLC Questions And Answers 8 September 7th, 2007 07:29 AM