Old September 10th, 2019, 12:30 PM   #1
bdb1324
Member
United States

bdb1324 is offline
 
Join Date: Jul 2019
Location: b
Posts: 13
Siemens IB to QB transfers

In Siemens s7-300 are IB and QB calls internal bytes or would QB17 overwrite Q17.0 through Q17.7 ect?
  Reply With Quote
Old September 10th, 2019, 12:45 PM   #2
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,181
QB17 would overwrite Q17.0 through Q17.7.



Similarly, QD16 would overwrite QB16-QB19 (which would be Q16.0-Q19.7 or QW16-QW18).
  Reply With Quote
Old September 10th, 2019, 12:51 PM   #3
bdb1324
Member
United States

bdb1324 is offline
 
Join Date: Jul 2019
Location: b
Posts: 13
Thank you that clears up a lot for me. So another example B#16#3F is in hex when it gets transferred to QB17 will it be in binary form or decimal or hex?
  Reply With Quote
Old September 10th, 2019, 01:28 PM   #4
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,181
Bin vs Hex vs Dec is just how you view the number. It's all the same to the PLC. You pick how you view it, just like you can in the windows calculator.
  Reply With Quote
Old September 10th, 2019, 02:35 PM   #5
bdb1324
Member
United States

bdb1324 is offline
 
Join Date: Jul 2019
Location: b
Posts: 13
I guess what I meant was will it store it as

qb17 0 0 0 0 0 0 0 3F

qb17 0 0 0 0 0 0 0 63

qb17 0 0 1 1 1 1 1 1
  Reply With Quote
Old September 10th, 2019, 03:01 PM   #6
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,181
Quote:
Originally Posted by bdb1324 View Post
I guess what I meant was will it store it as

qb17 0 0 0 0 0 0 0 3F

qb17 0 0 0 0 0 0 0 63

qb17 0 0 1 1 1 1 1 1

Let me ask a question then. What do you think Q17.0 represents?
  Reply With Quote
Old September 10th, 2019, 10:24 PM   #7
sigmadelta
Member
Canada

sigmadelta is offline
 
Join Date: Apr 2016
Location: From Canada - Living in Bulgaria
Posts: 1,181
Quote:
I guess what I meant was will it store it as

qb17 B#16#3F

qb17 63

qb17 2#0011_1111
Yes. Think of it like representing 1 meter = 100 cm = 1000 mm.
__________________
Automation Programmer
PLC / HMI / SCADA / SQL
System Upgrades & Conversions
------------------------
Visit: contrologica.com
Email: info@contrologica.com

Last edited by sigmadelta; September 10th, 2019 at 10:28 PM.
  Reply With Quote
Old September 10th, 2019, 10:48 PM   #8
sigmadelta
Member
Canada

sigmadelta is offline
 
Join Date: Apr 2016
Location: From Canada - Living in Bulgaria
Posts: 1,181
Like mk42 said, in Windows Calculator:

63 DEC = 3F HEX = 0011 1111 BIN

They are all the same value represented in different numbering systems.
Attached Images
File Type: png Windows_Calcluator_Programmer.png (16.2 KB, 44 views)
__________________
Automation Programmer
PLC / HMI / SCADA / SQL
System Upgrades & Conversions
------------------------
Visit: contrologica.com
Email: info@contrologica.com
  Reply With Quote
Old September 11th, 2019, 03:40 AM   #9
parky
Member
United Kingdom

parky is offline
 
Join Date: Oct 2004
Location: Midlands
Posts: 1,232
I am perplexed by this QB is the same. i.e. Bit Q 0.0 is the first bit of QB0 so why would you transfer it, on the other hand transferring a IB to QB will overwrite the QB with the exact data in IB. If you are talking about I/O refresh then PIB (the actual real Input Image) transferred to IB will update the internal image at that period in time, The real input image is transferred to the internal image outside the normal scan of the code (Dependant on type of PLC) i.e. Before or after code scan the input/output image is updated. If the program scan is 100ms then the Images will be updated every 100ms, however calling a block that updates the I/O image (L PIB 10 T IB 10) will update it immediately, There can be various ways to update, Calling the update function in an interrupt or by calling the FB many times in OB1 between calls to other blocks. Calling it in interrupt will update either in I/O interrupt (update when real inputs change) or if say scan of PLC is 100ms calling the block many times in OB1 will update in the following manner
OB1 total scan of PLC 100ms
JU PB X (5ms)
JU FB Update
JU PB y (10ms)
JU FB Update
JU PB Z (15ms)
JU FB Update
Would update the image after 5ms, 10ms & 15ms etc.
  Reply With Quote
Old September 11th, 2019, 05:31 AM   #10
sigmadelta
Member
Canada

sigmadelta is offline
 
Join Date: Apr 2016
Location: From Canada - Living in Bulgaria
Posts: 1,181
Quote:
In Siemens s7-300 are IB and QB calls internal bytes or would QB17 overwrite Q17.0 through Q17.7 ect?
IB and QB are not internal bytes - MB are internal bytes. QB 17 consists of Q17.7 to Q17.0 (most significant bit to least significant bit). 8 bits = 1 byte

IB is Process Image Input Byte
QB is Process Image Output Byte

PIB is Peripheral Input Byte
PQB is Peripheral Output Byte

The scan sequence for the S7-300 (with MMCs) is as follows (simplified for this thread):

Write to Process Image Outputs
Read from Process Image Inputs
Execute Code (OB1 & any other OBs for interrupts, timed interrupts, etc.)
Repeat

Peripheral Inputs and Peripheral Outputs are immediately read from and written to the physical I/O at the very spot in the program where they are encountered.

Process Image Inputs and Process Image Outputs are read from and written to the physical I/O at the beginning of the scan.

There isn't really anything more to it than that... other than you can have multiple Process Images in some CPUs, but that's a bit more advanced than the question of this thread.
__________________
Automation Programmer
PLC / HMI / SCADA / SQL
System Upgrades & Conversions
------------------------
Visit: contrologica.com
Email: info@contrologica.com
  Reply With Quote
Old September 11th, 2019, 10:10 AM   #11
bdb1324
Member
United States

bdb1324 is offline
 
Join Date: Jul 2019
Location: b
Posts: 13
Thanks everyone for the comments that was a huge help. The program calls FC41 to measure the width of a plate for blasting and painting. Once that is done the program uses a transfer from IB9 to QB17 if the plate is between a certain width if not the program transfers B#16#3F to QB17. Reason for the questions.

FC41 only gets called when the plate is at a certain position on the conveyor.

Thanks for all the information. They are transferring it to an Allen Bradley PLC and I am trying to understand what the Siemens PLC was doing. So very much appreciated.
  Reply With Quote
Old September 12th, 2019, 07:38 AM   #12
parky
Member
United Kingdom

parky is offline
 
Join Date: Oct 2004
Location: Midlands
Posts: 1,232
According to Siemens FC41 is a communication block (FTP) as standard, however it can be changed to another FC number, If it is the original then there must be some communications going on. FC 41 is also reported to be a PID (which if I remember correctly I have used). If you can open it, it may be that it is one created by the programmer. It seems a bit confusing to me. It sounds like they are not using interrupts for counting purposes (unless it is done elsewhere) but are transferring the data to outputs like some parallel interface i.e. a value that represents the size.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Siemens or Omron? Gromit LIVE PLC Questions And Answers 35 November 14th, 2017 09:44 AM
AdvancedHMI - Siemens PLCs S7-200/1200/300/400 Beta drivers BryanG LIVE PLC Questions And Answers 25 December 3rd, 2013 02:21 AM
Siemens to Allen Bradley sweetjohnny LIVE PLC Questions And Answers 4 April 20th, 2013 01:46 AM
Siemens 505 to Siemens S7 Rob S. LIVE PLC Questions And Answers 5 July 10th, 2012 07:37 PM
Transfer Data From Siemens PLC to AB PLC Danocane LIVE PLC Questions And Answers 8 September 7th, 2007 06:29 AM


All times are GMT -5. The time now is 07:42 PM.


.