Old September 11th, 2019, 06:03 AM   #1
Rson
Member
United States

Rson is offline
 
Join Date: Jun 2017
Location: Michigan
Posts: 175
Testing thermocouple inputs

So I have a project with a couple of thermocouple cards on an Allen Bradley L33ER rack. The instruments aren't due in for a little while, and I want to test out the signal high/low. I have an analog signal generator for mA and 0-10, but thermocouples send in a mV signal, correct?

Any good way to bench test these inputs? Is it as simple as making a voltage divider with a potentiometer reducing the voltage to the mV range?
  Reply With Quote
Old September 11th, 2019, 07:04 AM   #2
gtsuport
Member
United States

gtsuport is offline
 
Join Date: Feb 2005
Location: Grand Rapids, MI
Posts: 1,166
I have used this device with pretty good success.


https://www.amazon.com/Resistance-Cu...s%2C139&sr=8-3


Does quite a few different signal types.



gtsuport
  Reply With Quote
Old September 11th, 2019, 07:56 AM   #3
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,405
You can buy a cheap thermocouple for less than $10.00.


B
__________________
Knowledge is power, share the knowledge.
  Reply With Quote
Old September 11th, 2019, 08:07 AM   #4
mister x
Member
Canada

mister x is offline
 
Join Date: Jan 2019
Location: Canada
Posts: 76
This.

Do a 3 point check with a short piece of TC wire. 0C/room temp/100C.
  Reply With Quote
Old September 11th, 2019, 08:40 AM   #5
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 443
Better to use a specific thermocouple simulator since the signal at the analog input is the difference between the mV generated in the hot junction minus the mV of the cold junction.
It could also be done with a simple mV generator if you apply the difference of mV explained above.
__________________
Suppanel HMI
  Reply With Quote
Old September 11th, 2019, 10:26 AM   #6
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,592
If you use the correct TC extension wire, and you have a millivolt output meter.

Run copper wire from meter and twist together with the TC extension wire. Make sure you remember that Type K wire colors are Red=Neg and Black = positive.
Now get a glass of ice water (lots of ice) and insert the junctions you twisted together in the glass of ice. Now you have created a "cold Junction" at 32 degrees. The water will stay at very near to 32 deg. till the ice melts.
You can use the millivolt reference table from here to test the PLC module. And now you do not have to correct for the different temperature errors at the copper to Type K wire junction.
https://www.thermocoupleinfo.com/the...nce-tables.htm
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old September 11th, 2019, 10:49 AM   #7
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,244
Quote:
Originally Posted by NetNathan View Post
Make sure you remember that Type K wire colors are Red=Neg and Black = positive.
[/url]
FYI. In the US Type "K" is yellow(+) and red(-)

They vary though, see link

https://www.google.com/search?q=ther...hrome&ie=UTF-8
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb

Last edited by Mickey; September 11th, 2019 at 10:58 AM.
  Reply With Quote
Old September 11th, 2019, 12:58 PM   #8
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,592
Quote:
Originally Posted by Mickey View Post
FYI. In the US Type "K" is yellow(+) and red(-)

They vary though, see link

https://www.google.com/search?q=ther...hrome&ie=UTF-8
My mistake....thinking about Type S which I use a lot of...
Yes..
Type K is Yellow =Pos and Red = Neg

The OP is from US, so i did not see a reason for confusing things by giving him any of the overseas colors..
__________________
****Control Freak****
Net is where I be and Nathan is me.

Last edited by NetNathan; September 11th, 2019 at 01:00 PM.
  Reply With Quote
Old September 11th, 2019, 02:00 PM   #9
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,370
If they are 4 channel thermocouple cards, not 8, you can:
Make a copy of the project.
Change the IO Config to 4 channel input analog input cards
Test the program using mA or voltage signals.
Any changes needed make to the original also, ,or change the IO back to thermocouple.

If 8 channel inputs and you have extra slots on the rack you could put 2 analog inputs for a thermocouple input & change some addresses.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Old September 11th, 2019, 08:31 PM   #10
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 443
You don't need to create a 0C cold junction or use TC extension cable.
Measure the ambient temperature near the module, then look in the TC table the mV that correspond to the ambient temperature, then look the mV for the temperature you want to simulate and apply the difference between the two voltages in the module terminals.
__________________
Suppanel HMI
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Logix 5000 + Phoenix Thermocouple Module cking2729 LIVE PLC Questions And Answers 5 January 26th, 2017 05:01 PM
GuardLogix Safety Programing (L72) - Dual Channel Inputs kdcui LIVE PLC Questions And Answers 0 January 6th, 2012 10:36 AM
Thermocouple signal spiltter - got such thing? flyers LIVE PLC Questions And Answers 15 April 13th, 2007 09:20 PM
Thermocouple readout fluctuations leitmotif LIVE PLC Questions And Answers 18 March 5th, 2005 08:58 AM
High Density IO TimeFluxCap LIVE PLC Questions And Answers 13 January 22nd, 2005 09:28 AM


All times are GMT -5. The time now is 07:40 PM.


.