Monitor AB PowerFlex heatsink temp.
Is there a way to pull the heatsink temp from parameters to the PLC? I've had a couple critical drives fault recently for failed heatsink fans. We have them on a PM now, and I know you can set alarms for service life but that won't catch a premature failure. Any ideas?
|
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
as long as the fan is turning above some minimum speed the temperature doesn't matter. monitor whether the fans are running, e.g. a flashing light if the fan blades, or airflow, stops.
There's got to be a simple circuit to do that.
__________________
_ Brian T. Carcich i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Feb 2021
Location: USA
Posts: 9
|
Powerflex 753 has the following parameters available through datalinks, I would start here.
941 IGBT Temp Pct 942 IGBT Temp C 943 Drive Temp Pct 944 Drive Temp C It's been my experience that once the heatsink fans fail, you have about 10 minutes before the drive trips. Monitoring the heatsink temperature may not be the solution you are looking for. |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
The future of the Powerflex 4 and Powerflex 40 Drives | Rob S. | LIVE PLC Questions And Answers | 4 | October 29th, 2019 02:13 PM |
Powerflex 753 vfd fault | neilm | LIVE PLC Questions And Answers | 9 | July 9th, 2019 01:32 PM |
Connecting to PowerFlex 4 via 1747UIC Adapter | MY_USER.NAME | LIVE PLC Questions And Answers | 6 | August 29th, 2014 05:59 PM |
PowerFlex 400 PID Loop for DryCooler Fan / Temperature / Modbus | alexhk | LIVE PLC Questions And Answers | 1 | December 22nd, 2013 09:36 AM |
Error 75 on PowerFlex 70 | tjntjntjn | LIVE PLC Questions And Answers | 5 | June 12th, 2012 12:41 PM |