conductors passing over DIN rail

rpoet

Member
Join Date
Jun 2008
Location
New York, NY
Posts
536
Other than company spec and/or best practice, is there any code or standard (UL508A, etc...) violation if circuit conductors pass over DIN rail?

Example: Relay is mounted on DIN rail, and its socket has terminal screws on both sides. Wire duct is only on one side of relay. Can wires from the "other" side pass over the DIN rail and back into the wire duct?

Practically, I think we've all done it, especially in retrofit and repair situations. I have a colleague asking if there is a code/standard prohibition against doing so. I believe it looks sloppy and one should try to plan better especially in new panel builds, but it's sometimes unavoidable.

Thoughts?


Thanks,

rpoet
 
I’m not aware of any restrictions like that. UL508a does specify clearance for bending wires though. With small gauge and plenty of clearance it is a non issue most times.
 

Similar Topics

Hello all. So... last night this crept in to my mind. PLC lead times... Seeing that there is a lot of talk about the shortages producing...
Replies
30
Views
12,924
I have a branch circuit with the following motor and drive: Motor 1.1hp 480VAC VFD 1.5kW Normal Duty 2.0hp NEC 430 seems to suggest that I...
Replies
19
Views
4,836
Hi all, I'm trying to get a bom together for an R&D project. I have modbus devices that require 355mA for power plus communications. Does anyone...
Replies
3
Views
1,306
Im currently in a situation where our prefabricated copper twisted shielded pair (18awg) instrumentation cables are coming up short...
Replies
9
Views
2,670
Because of 3 or 4 posts with errors on this subject, this US National Electrical Code admonition needs repeating: NEC Handbook Article 430.22...
Replies
10
Views
5,797
Back
Top Bottom