Been a long time since i have done any actual electrical design and want to make sure i am doing this correctly.

I have 480VAC 3 phase available and i need a transformer that can supply me with 120VAC single phase(one line with neutral) at 20 amps on the 120VAC side. So my old school math says a 3KVA transformer will be good like this one:
acme Item Number CE3000F007

Does this sound correct? I would wire the primary side with L1 and L2 to H1 and H4 (leaving L3 out) from the available 480vac. then on the secondary side i would use X1 and X2 for my output.
 
Been a long time since i have done any actual electrical design and want to make sure i am doing this correctly.

I have 480VAC 3 phase available and i need a transformer that can supply me with 120VAC single phase(one line with neutral) at 20 amps on the 120VAC side. So my old school math says a 3KVA transformer will be good like this one:
acme Item Number CE3000F007

Does this sound correct? I would wire the primary side with L1 and L2 to H1 and H4 (leaving L3 out) from the available 480vac. then on the secondary side i would use X1 and X2 for my output.
20A x 120V = 2400VA, CPTs come in 2000VA or 3000VA, so yes, you picked the right one. Ground the X2 side of the secondary.
 
What !
On the high connection for 480v is L1 to H1, L2 to H4 and H2 to H3
there is 2 windings on the primary side
H1 and H2 are one coil 240V H3 and H4 are the other coil 240V
if you don't connect H2 to H3 the circuit will be open and no current will flow - not output
X1 and X2 for the output coil 120V if its a singe voltage output
X2 should be connected to the panel ground (Bonding) Require by UL to keep from getting a floating high voltage in the 120V line
 

Similar Topics

Sorry, not really PLC's. I have been going around and around trying to get a solid answer to my question and not finding anything that really...
Replies
15
Views
4,920
I have an application that has 3 24VDC motors. Each motor pulls around 10 amps, but none of them will run at the same time. If I fuse them...
Replies
20
Views
5,752
Hi Everyone, I am a student and am new here and I have a question that is not a plc topic. I would like to know how to go about sizing fuses on...
Replies
9
Views
3,850
When using a transformer sizing tool like this http://www.csgnetwork.com/xformercalc.html when it ask if it's a single phase or 3 phase how does...
Replies
13
Views
4,688
I have a big system to quote. This system will have 3 single phase power supplies fed off of a 3 phase transformer. 1 ea. on A-B, B-C, C-A. So how...
Replies
14
Views
5,154
Back
Top Bottom