Good morning all. Need help on communicating between an existing Compactlogix and 20 Powerflex 4 VFDs. There are no special communication cards in the VFDs. The 1769 L33ER is communicating to a 1747-AENTR via Ethernet. Is there a device that will allow creating an RS-485 network for all of the VFDs that will then interface nicely on Ethernet to get into the CompactLogix. Mostly want to control frequency command but would be nice to get some feedback from the drives.

I see several devices (MB-Gateway, Digi One IAP) but not sure if they will do what is needed.

Thanks for any advice.
 
1769-SM2. It offers 3 channels, 5 drives per channel. So you would need 2 cards.

You will also need some of the following connectors:
AK-UO-RJ45-TB2P (I believe they are a 5 pack)

We use belden 3105A to wire them.
 
1769-SM2. It offers 3 channels, 5 drives per channel. So you would need 2 cards.

You will also need some of the following connectors:
AK-UO-RJ45-TB2P (I believe they are a 5 pack)

We use belden 3105A to wire them.
Also, you can use that to communicate to one drive, then set up a daisy chain sub network of up to 32 drives using their inherent RS485 ports. The down side is that if the master drive goes down, you lose the entire sub net, but if they are all on the same machine and must run together anyway, that’s not usually a problem.
 

Similar Topics

I am facing a communication problem between 1769-SDN and powerflex 700.Compact logix PLC is showing Powerflex 700 node is not ready even with...
Replies
9
Views
5,467
Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400 Messaging but don't see the N...
Replies
0
Views
52
How to remove faceplate from power flex 753 and not shutting the system down. What parameters should i change?
Replies
1
Views
73
Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
Replies
6
Views
182
Powerflex 755, running 2 weeks, and faulting with code 17 input phase loss.
Replies
3
Views
147
Back
Top Bottom