I'm a very new user of Allen Bradley contrologix.
Last night we have a problem with our newly installed control panel (Allen Bradley Contrologix). The communication between the processor and the flex I/O suddenly failed resulting our machine down.
Indications on all the flex I/Os were healthy. The redundant controlnet network looked normal. When we checked in the RSLogix5000, it mentioned about module fault code 16#0317. Based on the help file, we need to download the RSnetworx, and we did.
That solved the problem but didn't promise permanent solution. We are still in the dark on what caused the problem.
The only abnormality that we've found was the 1756-CNBR/E was configured as 1756-CNBR/D. It has been running for almost 2 months after its installation. So we assume that it was not the root cause. The controller did indicate module mismatched.
Can this be a problem? Any similar experience by other users?
Thank you.
Last night we have a problem with our newly installed control panel (Allen Bradley Contrologix). The communication between the processor and the flex I/O suddenly failed resulting our machine down.
Indications on all the flex I/Os were healthy. The redundant controlnet network looked normal. When we checked in the RSLogix5000, it mentioned about module fault code 16#0317. Based on the help file, we need to download the RSnetworx, and we did.
That solved the problem but didn't promise permanent solution. We are still in the dark on what caused the problem.
The only abnormality that we've found was the 1756-CNBR/E was configured as 1756-CNBR/D. It has been running for almost 2 months after its installation. So we assume that it was not the root cause. The controller did indicate module mismatched.
Can this be a problem? Any similar experience by other users?
Thank you.