Powerflex 755 - 13035 problem

Hello


Im currently working with a AB powerflex 755 drive. I matched the drives and created database, downloaded add on profiles and tried to change almost every parameter there is and still, i get this 13035 problem, it says that adapter gets IDLE packets. What does that even mean?



Right now, drive is connected through stratix 8000, and even though i heard about IGMP snooping i've tried connecting directly with plc and still same massage.





There is a massage on display like "not enabled" does it mean that drive is not enabled or?
  Reply With Quote
Old June 22nd, 2018, 12:17 AM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,288
Welcome to the PLCTalk Forum community !

The PowerFlex 755 has an onboard EtherNet/IP port, which is considered "DPI Port 13". The fault code number includes that port (13) along with the fault (035).

A "Net Idle Fault" usually means that the packets being sent by the controller to the PowerFlex drive include a flag indicating that the connection is in Idle mode.

Most of the time, that means that the ControlLogix controller is itself in PROG mode. That doesn't break the I/O connection (inputs are still being exchanged) but it does cause the drive to go into Idle mode.

By default, drives will fault when their connection goes Idle. You can configure the drive to simply Stop on idle mode.

The most common instance where I see this complaint is during commissioning when you're downloading programs to the ControlLogix. When the ControlLogix goes into PROG mode, all the drives fault. You don't notice until you get the controller running again and the drives are faulted and need to be reset.

The Knowledgebase also has an article (Article 517712, Access Level: Everyone) saying that certain versions of PowerFlex 755 firmware require an Ethernet switch with a specific type of Quality of Service (QOS) flag.
  Reply With Quote
Old June 22nd, 2018, 12:45 AM   #3
matatata
Member
Croatia

matatata is offline
 
Join Date: Aug 2017
Location: Croatia
Posts: 23
when i download software and put it in run, i cant clear drive of faults...


how would a parameter look like to put a drive into stop instead of fault on idle communication?
  Reply With Quote
Old June 22nd, 2018, 02:08 AM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,288
Quote:
when i download software and put it in run, i cant clear drive of faults.
Usually simply pressing the "STOP" button on the keypad will clear the faults, or cycling a discrete input that is configured for "Stop/Clear Faults".

If those do not clear this specific fault, then there may be something wrong with the Ethernet configuration, like the QOS setting I mentioned.

A-B drives can react to Idle state or to a network Fault condition separately. They can be set up to declare a Fault, or simply to Stop, or to keep running, or even to start and run at a specific speed !

On the PowerFlex 755, look at the Programming Manual (750-PM001), in Chapter 5, for the Embedded EtherNet/IP Port 13 Parameters.

Parameters 54 and 55 are the Comm Fault Action and Idle Fault Action. I prefer to set both of those to "1" to Stop the drive instead of Faulting it.
  Reply With Quote
Old June 22nd, 2018, 07:54 AM   #5
matatata
Member
Croatia

matatata is offline
 
Join Date: Aug 2017
Location: Croatia
Posts: 23
thank you very much! will try it today
  Reply With Quote
Old June 22nd, 2018, 11:20 AM   #6
matatata
Member
Croatia

matatata is offline
 
Join Date: Aug 2017
Location: Croatia
Posts: 23
its connected to the 1756-en2t module, how to see if the qos is enabled on that module?
  Reply With Quote
Old June 22nd, 2018, 12:04 PM   #7
matatata
Member
Croatia

matatata is offline
 
Join Date: Aug 2017
Location: Croatia
Posts: 23
I set those parameters to stop and nothing changed... like you've said, communication is going on normally but since i dont get the status that drive is ready i cant control it...
  Reply With Quote
Old June 22nd, 2018, 12:58 PM   #8
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 52
Are you using a safe torque off add on card in the drive? If so "not enabled" means that the safety is open or possibly the safety jumper is still installed. Thats the only time ive ever seen that display. Typically if a stop command is being given by the drive or PLC it will say "stop asserted"
  Reply With Quote
Old June 22nd, 2018, 01:00 PM   #9
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 52
review this

https://rockwellautomation.custhelp....ail/a_id/62222

PowerFlex 755 Not Enabled troubleshooting
62222 | Date Created: 06/12/2009 | Last Updated: 01/11/2018
Access Level: Everyone
  Reply With Quote
Old June 22nd, 2018, 03:03 PM   #10
matatata
Member
Croatia

matatata is offline
 
Join Date: Aug 2017
Location: Croatia
Posts: 23
Quote:
Originally Posted by _Dock_ View Post
Are you using a safe torque off add on card in the drive? If so "not enabled" means that the safety is open or possibly the safety jumper is still installed. Thats the only time ive ever seen that display. Typically if a stop command is being given by the drive or PLC it will say "stop asserted"

yea im using this add on card, today they went though connections and it seems like every safety contact is not energized, im going to wait for them to fix this.
  Reply With Quote
Old June 22nd, 2018, 06:32 PM   #11
matatata
Member
Croatia

matatata is offline
 
Join Date: Aug 2017
Location: Croatia
Posts: 23
works now! safety inputs were causing problems
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Powerflex 755 rev 10.02 not showing in rslogix 5000 rev 20.01 edwardeduful LIVE PLC Questions And Answers 6 November 30th, 2017 01:12 PM
Powerflex 755 not outputting over motor nameplate current remlapw LIVE PLC Questions And Answers 3 January 20th, 2017 11:03 AM
Problem using PowerFlex DC in voltage feedback mode accidentalengineer LIVE PLC Questions And Answers 9 December 15th, 2016 07:14 AM
Integrating PowerFlex 755, Incremental Encoder, & Proximity Sensors into Ladder Logic jake4eng LIVE PLC Questions And Answers 7 September 29th, 2016 04:17 PM
PowerFlex 700 Problem.... JoseM LIVE PLC Questions And Answers 2 September 14th, 2012 11:26 AM


All times are GMT -5. The time now is 01:25 PM.


.