Hi all
I want your advise in my problem:
I have an old plc (Arcom device with Isagraph program) which used to be monitored with Intouch SCADA , but the license of this SCADA will expired at this year end . I asked in this forum for an advise to monitor the PLC with Wncc and I was advised to use an OPC serve because the PLC uses Modbus RTU Protocol which isn't included in Wincc.
I decided to use kepware OPC server and I succeded in making connection with my RTU but I found a problem that the addresses in my PLC for the pressure and temperature monitoring are 30001 to 30019 but in kepware the addressing must be 300001 (with an extra 0) so the reading on Wincc wasn't correct .
I didn't know how to make the addresses match my PLC addresses.
I can't modify the PLC configuration
The temperature and pressure analog signals are (4-20 mA)
Is there anybody that can help me please …. I'll appreciate any advice.