ControlLogix Redundancy Firmware

CEN

Member
Join Date
Dec 2018
Location
Pennsylvania
Posts
22
Hello,
I recently ran across a ControlLogix L63 processor that is running firmware version 19.52. After reviewing the rack configuration and controller configurations it doesn't appear to be set up for redundancy.....(box not checked for redundancy, no other controller in IO Configuration and no redundancy modules). Am I missing something or is this just the wrong firmware? Should/Could I just flash it to v19.015? Anyone ever seen this before.
THanks in advance.
 
it should be obvious if it set up for redundancy. The redundancy module would show if it's in sync or not.

You also said "a ControlLogix processor". So, is there another processor in physical redundant configuration?
 
Nope, no other processor and no redundancy module. Must have had the intention of adding this feature originally but never did. I'll flash it to v19.015, just checking my sanity.
Thanks,
 
The Rockwell recommendation is to not load redundant firmware on non-redundant processors, although it seemed to work for us for a while. I would flash back to the non-redundant version.
 

Similar Topics

Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
Replies
1
Views
60
Hello, My associate and I are trying to sync up two ControlLogix racks (7-slot chassis) with identical modules. We are able to see the secondary...
Replies
4
Views
185
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
Replies
0
Views
75
Hi Guys, Is it okay to have Redundancy ControlLogix Processor IP address set to DHCP? I had Static IP address on it but removed it via RSLinx...
Replies
3
Views
226
Hi Guys, For a Redundant Controllogix L81E with EN2TR, on a Device Level Ring; does the Controller also require IP address assigned?
Replies
2
Views
163
Back
Top Bottom