Automation Direct DL06 plc

dbh6

Lifetime Supporting Member
Join Date
Jan 2013
Location
Central, NJ
Posts
552
A customer of mine sent me a hard copy printout of the program, I'm modifying the printout program and sending it back to him to make the necessary changes I made into the plc. My question is, is their a internal coil that we can use to disable a rung kind of like an AFI instruction in the Allen Bradley world, sure I can write up my own always false bit, but I want to know if such a bit or instruction already exists thanks
 
. My question is, is their a internal coil that we can use to disable a rung kind of like an AFI instruction in the Allen Bradley world, I want to know if such a bit or instruction already exists thanks

SP1 = always on (contact)
SP2 = always off (contact)
 
Just for reference see the start of Appendix 'D' the the DL06 manual.

The ones I use most are:

SP0 - First Scan
SP1 - Always ON
SP2 - Always OFF

Check out this area. Very useful stuff there.
 

Similar Topics

Hi all, I am making a test rig to be able to wire in any DL06 (or DL05) And create a HMI in red lions crimson 3.1 to test all the inputs and...
Replies
4
Views
923
Hi everyone, I have a DL06 I'm trying to get some historical info off of. I don't have access to the actual PLC, but I have the program. I'm...
Replies
0
Views
1,155
I'm new to this software, and just recently installed an F0-04 thm thermocouple card to this plc. I wrote the logic according to instruction...
Replies
3
Views
1,536
I am new to PLCs just started doing this about a month ago. I want to write a ladder program using directsoft5 for DLO6 . The program should have...
Replies
10
Views
4,286
I've been out of programming PLC's for a 5 years, only some minor programming experience with some AB's and I've got myself into a small project...
Replies
1
Views
2,136
Back
Top Bottom