1734-AENTR Input light issue
Leukic
Oct 2018
Leesville
93
Gaurdlogix 5380 tied into 1734-AENTR. Safety scanner ossd1 and ossd2 are in I0 and I1 respectively. Common is hooked to 4&5. When we reset the scanner we get 24vdc from the scanner at the terminals of I0 and I1. But niether input shows to light up nor swap states in the program. Kinda stuck on this one. i may try to swap in a new input module and see if it works.
You probably need to set the "Point Mode" for the input points in the software?
Without this set the inputs will be inactive.
Go the the module properties for the 1734-IB8S and then to the "Input configuration" tab.
Under "Point Mode", select the Safety function for the individual input points.
Usually for a light curtain or similar you will select "Safety".
You also setup for Single or Dual function here with "Point Operation".
Regards,
George
Regards,
George
I found it. Just as I read you reply a little bit ago. When our engineer set up this stuff under config he forgot to set the status of the inputs they were set as NOT USED. Not sure why I didnt check that. Could because he said it's good to go haha. Thanks Geospark
The Input channel LED will also remain OFF if the module isn't configured yet, or if it's configured incorrectly for the inputs.
Did you inadvertently associate either of the Test Output signal sources with the inputs ? The inputs would be expecting to see the pulse train from the Test Output, not a steady 24V signal (which would indicate a short to 24V).
Otherwise your wiring sounds correct for a light curtain or safety scanner connection, like the example on Page 62 of the POINT Guard I/O User Manual.
edit: answered correctly while I was looking at the user manual and contemplating coffee.
Thanks Ken!
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
115
Hello all. I have a remote that uses a 1734-AENTR series C. We had to change it to a new one and, after adjusting the IP and number of slots...
16
452
The issue we have is that the IT2I thermocouple card and the RTD temperature sensor card connected through a point IO AENTR is constantly trying...
477
Hi guys, I have just recently purchased a 1734-AENTR module so that I could learn how to configure it through LogixDesigner and establish comms...
280
Hi there! I've been looking for some fault codes table for the 1734-AENTR adapters, since I'd like to show a message in HMI with some...
565