kjacoby
Member
Good Morning. I am fighting a time sync issue between two machines on the same network. One machine has kinetix 5500 servo drives, and the other has a power flex 527. I have a problem where if one machine drops off the network, the other machine will get a control connection fault on the servo, or the powerflex drive. I have been fighting this for a couple months now. To resolve the issue on the machine with the 5500 drives, I need to do a fresh download to get them back in sync with the PLC. I have played around with the master override, and tie breaker, but it just changes which plc is the grand master.
Is there a way to have each plc their own grand master, so they are not fighting each other on the same network?
The main issue last night was a fan was plugged into the same circuit as our plant network, tripping the breaker. When the network switch powered back up, we lost the sync on the other machine.
Any suggestions would be greatly appreciated.
Kenneth
Is there a way to have each plc their own grand master, so they are not fighting each other on the same network?
The main issue last night was a fan was plugged into the same circuit as our plant network, tripping the breaker. When the network switch powered back up, we lost the sync on the other machine.
Any suggestions would be greatly appreciated.
Kenneth