Digital offset on analog input
wildcatherder
May 2009
Morro Bay
168
On a Micrologix 1100 analog input, I appear to be getting an internal offset of about 11 counts out of 1023.
Running the program from RSLogix, when I look at N7:35, which is only written by the analog input, I see 6 counts out of 1023 when the analog input is shorted at the PLC input. If there is no applied input (and the short removed) I see 11 out of 1023 counts.
The measured input voltage in this case is .001 volts.
Does someone know where this offset comes from? It appears to be completely internal to the PLC.
What is the stated accuracy?
6/1023 * 100 = 0.5% of zero reading.
Is it really 1023, so 10 bit?
10-bits input
Overall accuracy is shown as +/- 1% full-scale, so that is 10 out 1023 and is good as it gets.
We were using the Micrologix 1000 with 16-bit input but switched because the 1000 is being discontinued.
Well, that's another mystery solved.
Thank you, G. McCormick for your assistance in this matter.
Question to anyone with ideas about my thoughts on upgrading a very vintage timer, which is being used to switch between 2 5hp domestic water...
435
I have a PLC type PM856 from ABB with some I/O modules and I get an error from the Digital Inputs model type DI801. The unit status shows error...
264
I am monitoring two BMXDDO3202K digital outputs for their behaviour, they are each for opening and closing, and so the on time affects how far the...
284
On the laser displacement sensor now connected to my PLC, the manual says 4mA=643 and 20mA=64,877. However, I checked with a Fluke, injecting...
888
I'm new to S7/TIA. There's no devices connected to the PLC yet. I've got a laser measurement sensor (Micro-Epsilon optoNCDT 1220). From the...
18
2,951