It seems as if some people are getting hung up on the term "risk assessment". Does it have to have an engineering stamp on it? (That would give it more clout than say, the floor sweeper signing off on it.) I don't think so: rules may be different all over. What it requires is a thorough examination by all involved. Google the term. A concientious look from multiple viewpoints (supervisors, operators, maintenance personnel) using a standard risk check - basically a probability of injury and severity are the concerns. I don't pretend to know the law. What I do know is that in the eyes of the Ministry of Labour in Ontario, if there is no paperwork for the R.A. it didn't happen. If your not sure where you or your company stands, call a lawyer before the accident happens.
  Reply With Quote
Old February 19th, 2020, 07:08 AM   #32
Rson
Member
United States

Rson is offline
 
Join Date: Jun 2017
Location: Michigan
Posts: 345
When it comes to sub-machine wiring, the 'Best practice' in my experience is for each machine to provide it's own E-stop condition AND:

1. The ability to tie another system into the E-stop condition (ie - extra terminals with jumpers in addition to the E-stop on a safety relay for example)

2. The ability to send the status of the machine's E-stop to another system. (ie - a spare set of contacts on the safety relay or signal from both aux safety relay contacts)

At that point, a proper risk assessment will determine what each machine's E-stop should do - shut the line down or stop just it's own machine.

Either way, a main station should be able to monitor if the machine is in an e-stop condition and alert the other machines or operators appropriately. This could vary wildly depending on the intended process.
  Reply With Quote
Old February 19th, 2020, 07:29 AM   #33
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 14,468
Quote:
Originally Posted by Rson View Post
When it comes to sub-machine wiring, the 'Best practice' in my experience is for each machine to provide it's own E-stop condition AND:

1. The ability to tie another system into the E-stop condition (ie - extra terminals with jumpers in addition to the E-stop on a safety relay for example)

2. The ability to send the status of the machine's E-stop to another system. (ie - a spare set of contacts on the safety relay or signal from both aux safety relay contacts)

At that point, a proper risk assessment will determine what each machine's E-stop should do - shut the line down or stop just it's own machine.

Either way, a main station should be able to monitor if the machine is in an e-stop condition and alert the other machines or operators appropriately. This could vary wildly depending on the intended process.
+1
This is a very important point, often ignored.

A practical tip:
When you tie in external safety contacts to your safety relay, and provide contacts from your safety relay for an external system to use, you must think about who/how the safety relay is reset. If the external system is not just one or a few E-stop buttons, but is actually a safety system with safety relay(s), then there is the risk of a catch-22 situation. Your safety relay is deactivated because the external contacts are deactivated, which deactivates the external seafety relay, which deactivates its contacts, .....etc.
What we do is to have at least one safety relay dedicated for external safety system. This safety relay auto-resets in our system. When an external safety stop is activated, the resetting must happen in the external system.
Conversely, we inform in our documentation that our contacts must be reset in our system, and the external safety system should auto-reset.
__________________
Jesper
See my profile interests for Q&A
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PowerFlex 40P External Stop Button MY_USER.NAME LIVE PLC Questions And Answers 2 September 10th, 2014 04:37 PM
e-stop question joeparrish LIVE PLC Questions And Answers 16 October 26th, 2010 03:28 PM
OT: Diodes in control circuits? plchacker LIVE PLC Questions And Answers 66 November 26th, 2007 06:52 PM
Manual/Auto jthornton LIVE PLC Questions And Answers 9 October 5th, 2006 01:40 PM
VFD Standard labingtone LIVE PLC Questions And Answers 11 January 31st, 2003 07:28 PM


All times are GMT -5. The time now is 02:43 AM.


.