Is a series of 4 e stop mushroom pushbuttons a true estop if it does not reset and does not use a safety relay?
When any of these buttons are pushed the safety rated red allen Bradley contactor opens above the motors normal contactor.
Do all estop circuits have to have a reset circuit to be classified as a estop?
 
wire them all in series, and wire them to a master control relay. If any one is pushed, then the mcr opens and kills all control power. When you reset the e-stop, the system has to be restarted.
 
wire them all in series, and wire them to a master control relay. If any one is pushed, then the mcr opens and kills all control power. When you reset the e-stop, the system has to be restarted.
And at best it will only be a category 1 system
 
Check out this PDF. Don't confuse the type of Stop with the category of the safety circuit.

A Category 1, while generally safe, can fail (and 'fail' means failure to stop the machine) if only one part fails to work as normal.

The whole point of safety is confidence that, once started, the machine can be stopped. The next point that it won't be allowed to start if any of the safety components are faulty.

You can't rely on components that, in order to turn off, depend on a spring. Springs break.

The higher categories are used as it is more possible that a machine can harm or kill an operator. Read carefully and take the examples to heart.
 
It depends upon your local legislation, here in the EU a E/Stop should have a positive locking action which in turn needs a positive action to reset it, automatic resets are,nt normally used for emergency stop circuits. so in essance, wired into a pilz unit with a reset circuit, unless it,s a safety plc you can,t wire them into there and use normal logic to control it !!

I,d do alot of reading upon on the subject purely because it,s safety and you could be dealing with somebodys life !!

Regards

JV
 
Is a series of 4 e stop mushroom pushbuttons a true estop if it does not reset and does not use a safety relay?
When any of these buttons are pushed the safety rated red allen Bradley contactor opens above the motors normal contactor.
Do all estop circuits have to have a reset circuit to be classified as a estop?
the basic principle of a safety system is to protect people.
the level of protection is as per the PDF that Bernie has directed you to.
Depending on what category you need.
Consider your contactor - the red series is fine but what happens if the contracts weld closed - how do you stop the motor or drive system.
ask yourself questions
If someone could get cought - how badly (risk analisys)
If the E/stop button fails - how do you Know it has failed
If a contactor fails - what can you do.
Dont forget mechanical / stored energy (Hydraulics Pnuematics)

At the end of the day there are many specialists that will assist you with safety systems, they are also insured to do so.
this is a better approach.




If
 

Similar Topics

I am trying to combine an auger filler with a packing machine. Neither of the 2 machines have a proper safety circuit. The power feed in is...
Replies
10
Views
4,803
The health-care and the machine automation worlds hardly ever cross-over. We don't hear of PLCs (or anything programmable) being used in medical...
Replies
9
Views
2,820
Hello again! I am looking at using the new AB 440RD22R2 next gen safety relay with Dual inputs and 2 outputs. I want to have one input be a non...
Replies
12
Views
4,749
Just as the title says, I’m looking for a reference as to why estops are normally setup with two separate contacts, one NC and another NO. Any...
Replies
9
Views
2,518
Hello, Should ESTOP circuits de-energise the control circuit or the power circuit to a motor? I want to put multiple ESTOPs to a safety relay...
Replies
4
Views
1,946
Back
Top Bottom