Old June 4th, 2009, 05:39 PM   #1
MCB
Member
United States

MCB is offline
 
Join Date: Jun 2009
Location: Pittsburgh, PA
Posts: 5
RSLinx Classic Crashes PLCs When Using Ethernet/IP Driver

I had an interesting problem at a customer's site today.

He has RSLinx Classic Professional version 2.50.00.20, and is using the Ethernet/IP driver to communicate with the PLCs. He is also using the Ethernet driver with individual IP addresses to talk to the different VFDs, which are from 192.168.0.30 though 192.168.0.38 (Both drivers configured are, however, on the same subnet. The Ethernet/IP driver configured to browse a remote subnet at 192.168.0.20, subnet 255.255.255.0)

In RSWho, if you were to simply just expand the tree that is the Ethernet/IP driver, all PLCs (there are 3 CompactLogix PLCs) on that subnet will completely lock up, as that is what I was told. He would then have to go power cycle the PLCs to get them to come back online.

Then after they power cycled the PLCs, they were able to see it in that RSLinx tree, and be able to get online. Say they would make changes to the program live in RSLogix5000 by adding a new tag. Then that would cause all of the PLCs on the network to lock up again, and be restored only after power cycling them.

I personally have not witnessed the PLCs crashing like that, and could not experiment today while I was there....




However, with my laptop running RSLinx Classic Gateway version 2.54.00.11, I was able to get online just fine. However, I used just the plain Ethernet driver, and added the IP addresses myself. I was also able to get online using RSLogix5000 with the processor with no problems.

I was unable to experiment with other drivers on the customer's PC today, as we were afraid of again crashing the PLCs...

The PLCs are all CompactLogix L32E.


So my question is: Is it the Ethernet/IP driver in RSLinx on the customer's computer causing the problem? Or is there something else configured improperly in my scenario above?


Thanks,

Mike B.
  Reply With Quote
Old June 4th, 2009, 07:22 PM   #2
peoplehouse
Member
United States

peoplehouse is offline
 
Join Date: Jan 2009
Location: California
Posts: 117
Is this an existing system that has been around for awhile or is it fairly new. I've had an experience with linx classic that when I installed it on my desktop to run an excel HMI it would crash my computer. I had to remove the software then reinstall. Just a guess
  Reply With Quote
Old June 4th, 2009, 09:03 PM   #3
dmroeder
Lifetime Supporting Member
United States

dmroeder is offline
 
dmroeder's Avatar
 
Join Date: Apr 2006
Location: Vancouver, WA
Posts: 2,077
Sounds to me like duplicate IP addresses on the network. It could be possible that it doesn't cause much of a problem until Linx tries communicating with the device that has the same address, then the network goes screwy. Just a WAG.
  Reply With Quote
Old June 5th, 2009, 09:09 AM   #4
MCB
Member
United States

MCB is offline
 
Join Date: Jun 2009
Location: Pittsburgh, PA
Posts: 5
Quote:
Is this an existing system that has been around for awhile or is it fairly new. I've had an experience with linx classic that when I installed it on my desktop to run an excel HMI it would crash my computer. I had to remove the software then reinstall. Just a guess
The desktop computer itself doesn't crash. That continues to run flawlessly. However, it causes the PLCs to lock up completely.

The system has been installed within the last 2 years, doing the same symptoms as I stated above on the customer's desktop PC.



Quote:
Sounds to me like duplicate IP addresses on the network. It could be possible that it doesn't cause much of a problem until Linx tries communicating with the device that has the same address, then the network goes screwy. Just a WAG.
That is what I am thinking, as the Ethernet/IP driver would conflict with the Ethernet driver with the addresses 192.168.0.30 through 192.168.0.38.

I just wanted to be sure that might have been an issue before I make my next site visit and start making those changes. I am hoping that will resolve the problem.

I am going to do an experiment in house here and see if that causes the PLC to fault.
  Reply With Quote
Old June 5th, 2009, 01:51 PM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,293
Exactly what does "completely lock up" mean, from the customer's perspective ? I realize that failure to communicate might be as severe as an operating system crash from an operational standpoint, but it's not the same if you'r troubleshooting.

Have the controllers faulted, and have a flashing red or solid red "OK" LED ?

Are there changes to the indicatiors on the Ethernet port of the controller (Link, MS, or NS) ?

Are there other HMI devices accessing the controllers ?

Are the controller running MSG instructions or Produced/Consumed Tags ? Are there any ways to determine the status of that traffic ?

Do networked I/O devices (particularly the drives) lose their logical control from the controllers ?

Do the controllers not respond to HTTP or ICMP PING requests ?

Can the controllers be accessed using their serial ports ?

I use the EtherNet/IP and Ethernet Devices drivers all the time to access the same devices, and do not have any problems with them. I have ControlLogix and CompactLogix going back to 1997.

Is the PC's Ethernet interface actually on a different subnet from the controllers and the drives ?

My first two troubleshooting steps would be to use PING and a web browser to find out of the controllers are accessible using something other than CIP protocol.

I'd also check carefully the Connection count on the controllers and the CPU utilization of the Ethernet daughtercard. The symptoms you described seem consistent with the controllers being starved for connection resources or bandwidth, which are relieved by the power cycle.
  Reply With Quote
Old June 5th, 2009, 02:23 PM   #6
MCB
Member
United States

MCB is offline
 
Join Date: Jun 2009
Location: Pittsburgh, PA
Posts: 5
The customer only told us that the processors completely stopped and the plant pretty much shut down. Power cycling them brought them back up.

I was not able to perform any troubleshooting on site yesterday, as they could have their plant go down at that time.

So I currently do not know if the controllers faulted, or had Ethernet problems, etc.


But I can answer some of your questions:
1. For each of the 3 PLC cabinets, there is a Panelview Plus screen accessing their associated controller.

2. There are no MSG instructions in the program.

3. The VFDs do loose their control from the PLCs when this happens

4. There is only one desktop PC on this network with RSView/RSLinx/RSLogix5000, and it is on the same subnet as the controllers and drives. While I was there, RSView was running just fine on his PC.



That aside, on my laptop, I was able to see all of the PLCs in RSLinx, and I was able to go on RSLogix5000, upload the program to my computer, and view everything working. I did not try to add a tag or anything, but it was completely stable the whole time, including me accessing it in RSLinx.

On my next site visit, I will be able to troubleshoot this completely, even if it takes the plant down again.
  Reply With Quote
Old June 5th, 2009, 10:22 PM   #7
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,293
Wow, that's just a whole lot of weird. Adding a tag to one controller absolutely should not cause a different controller to fault.

A failure or "lockup" of the Ethernet daughtercard would break the I/O connections and make the connections to RSLinx and PV+ fail. An actual fault of the controller would do the same.

I'd take two tools with me on this:

1. The Fault Dump Utility from RA Tech Support. If the controller operating system is really failing, you can get some information out of the serial port. Do this before attempting to recreate the situation, and after.

2. A managed Ethernet switch with Port Mirroring. Capture the data going into the controller(s) when the RSLinx 2.50 browse is performed. Are you familiar with Wireshark ?

Get an RA Tech Support case going before you go onsite, so that you'll have someplace to send the dump files or capture files.

Last edited by Ken Roach; June 5th, 2009 at 10:28 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Open Source Ethernet/IP Drivers for A-B PLCs jctux LIVE PLC Questions And Answers 1 December 14th, 2008 05:34 PM
RSLinx DF1 frezes upon cable connect, SLC503 - no comms Alaskan LIVE PLC Questions And Answers 6 July 12th, 2008 03:11 AM
RSLinx problem registering definitions from PIUNSOL.INI Koos LIVE PLC Questions And Answers 0 January 13th, 2008 11:23 PM
RSLinx glaverty LIVE PLC Questions And Answers 6 February 10th, 2003 12:39 PM
RSLinx 2.4 Jiri Toman LIVE PLC Questions And Answers 5 January 4th, 2003 12:01 PM


All times are GMT -5. The time now is 05:03 AM.


.