RSView32 - Unable to write tag

Hi All,

Currently I am networking several PLCs together (SLC5/04, SLC5/05, ML1500) and used RSView32 to create real time visual manufacturing and monitor the inputs of each PLCs. The communication protocol I used here is Ethernet. Therefore, I had 1761-NET-ENI for SLC5/04 and ML1500 to communicate via Ethernet. I had created DDE/OPC topic for each PLC in RsLinx. So, I was able to monitor the PLCs I/O address in RSView32.

However, I am trying to write a value to a tag, but i was unable to do it. I use both toggle and set command in RSView32, and I can see RSLinx is sending packets to the specific PLC. But the PLC input didn't have any response.

Does anyone encounter any of this problem before?

Thanks

Regards,
Herbert
  Reply With Quote
Old March 10th, 2006, 09:46 AM   #2
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,093
Is there anything in the PLC programm writing to this input,bit,word
or whatever address it is you are trying to change. This may be over writing your RSView32 write,
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old March 10th, 2006, 09:55 AM   #3
hhuong
Member
United States

hhuong is offline
 
Join Date: Nov 2004
Posts: 58
Actually i just want to perform a simple task like turn on a specific input of a PLC.

For Example, I want to turn on the input I:1/0 of SLC5/04. I use Set command in the RsView32. At the bottom of the RsView32 stated "write value 1 to Tag'Input_1'". There is no error warning. I assume RsView32 was able to send out the command. But I guess the PLC didn't receive the command from RsView32.
  Reply With Quote
Old March 10th, 2006, 10:06 AM   #4
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,093
You can't do that, only the PLC can control its inputs and outputs.
You can write to binary,integers,floating points,timers,counters etc.
Not "I" or "O" maybe to outputs if the PLC is not controlling it but I would not do it.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb

Last edited by Mickey; March 10th, 2006 at 10:08 AM.
  Reply With Quote
Old March 10th, 2006, 10:13 AM   #5
hhuong
Member
United States

hhuong is offline
 
Join Date: Nov 2004
Posts: 58
You are right, Mickey!
I had made two mistakes here. The problems are:

First, I try to write a value to physical input and output which is not allowed. Second, when I try to write a value to a binary bit B3:0/0, the plc don't respond because in my program the binary bit was also controlled by Input. Therefore, the input overwrite my RsView write command.

Thanks for all the information, Mickey.
  Reply With Quote
Old March 10th, 2006, 10:22 AM   #6
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,093
Your Welcome
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RSView32 error: Unable To Start Tag Browser ladderlogix LIVE PLC Questions And Answers 4 December 31st, 2010 11:54 PM
Unable to Delete Tag in RSViewSE modicon2 LIVE PLC Questions And Answers 1 November 24th, 2006 01:50 PM
Organising folders in RsView32 Tag DB sparky64 LIVE PLC Questions And Answers 5 October 27th, 2004 03:15 PM
RSView32 Tag Database Addresses Eddie22 LIVE PLC Questions And Answers 8 August 3rd, 2004 10:58 AM
Panel View Pushbutton Clarity? ganutenator LIVE PLC Questions And Answers 15 July 3rd, 2003 10:26 PM


All times are GMT -5. The time now is 01:05 PM.


.