Beijers E1000 - Modbus Multiple Write Command

Philg

Member
Join Date
Jul 2006
Location
Adelaide
Posts
14


I currently have a E1101 talking across Modbus to a DSE 5220 Genset Controller using the following driver…



Com1 – modicon Master/Modbus Naster 4.04.01



I am able to read from the controller as the Driver uses the Modbus Multiple Read Command (03), but to write commands the controller required a Modbus Write Multiple Registers Command (16)



Ie… Multiple Command (Slave 10) should be “0A 16 ………”



At the moment when writing the E1000 Modicon driver is sending “0A 06 10 00 00 08 8D B7”



Is there any way I can get the driver to send a multiple write command ???

 
Thats good thanks - it's sending the "16" now... I have this problem with my installation of EDesigner that not everything in the windows are displayed (ie... options are cut off) which I think is to do with having a wide screen laptop. If I open it on a square screen the windows are all in the right proportion and options like the check box you just mentioned are accesible.

Have you ever come across this? Is there a fix ??
 
dse 5220 with rs485tors232 converter

Hi All,

I have tried to connect dse 5220 to my linux PC with modpoll as master application.
I used rs485 to rs 232 converter (sintech) and UTP cable (only 1 pair is used)
I put serial parameters :
-baudrate = 19200
-slaveID = 10
-parity = none
-stopbit = 2
-databit = 8
this is default value according to P810 software from DSE

I dont use termination resistor (120 ohm)

Always got timeout.

Any help would be much appreciated

Thanks
 

Similar Topics

I am trying to set up a E1101 to be a Modbus master to a Deep Sea Electronics 5220 controller. The DSE5220 has a RS485 connection. At the moment...
Replies
1
Views
6,475
Hello, Does anyone have any experience of using a small label printer with a Beijers E1000 Series HMI. I haven't decided on a particular model of...
Replies
2
Views
4,217
I am using an E1101 Beijers HMI touch screen HMI/GUI in conjunction with an FX3 PLC. The E-Designer software is version 7. The Alarms screen 990...
Replies
3
Views
4,361
Is anyone aware of whether you can access the FTP data (trend backup data) through the PPP connection ? I connect using the PPP connection, and...
Replies
3
Views
3,222
I have two Trend graphs but only want to back one of them up to the Compact Flash card. Under "System Settings\Commands" according to the manual...
Replies
2
Views
4,337
Back
Top Bottom