Question about star-delta control circuit diagram

Wye delta

K1T ( n.c.) is in wrong location. It should be on 2nd rung to open k1 resulting in k3 being energized by k1 interlock . Basically transition from wye to delta connection.
 
K1T ( n.c.) is in wrong location. It should be on 2nd rung to open k1 resulting in k3 being energized by k1 interlock . Basically transition from wye to delta connection.
welcome to the site
Can you please check the date of the last post

2009 is very old
 
Hi Shilpesh
From your circuit diagram,K1 is for STAR connection.For Star delta Starter,The first sequence after you press ON push button is K1 MUST energize first before K2.Why? because if K2 energize first before K1 it can cause the spark and can damage the contactor. The Key point for star connection is to start the motor in 240 Volt to reduce high in rush ampere and build a torque..after a motor achieve 80% running..it switch to Delta.It mean the motor running with full capacity ( 415 volt )..For more detail,please read some post about star delta starter below :-

http://www.electricneutron.com/electric-motor/star-delta-motor-connection/
http://www.electricneutron.com/motor-control/star-delta-starter/
 
Hi Shilpesh
From your circuit diagram,K1 is for STAR connection.For Star delta Starter,The first sequence after you press ON push button is K1 MUST energize first before K2.Why? because if K2 energize first before K1 it can cause the spark and can damage the contactor. The Key point for star connection is to start the motor in 240 Volt to reduce high in rush ampere and build a torque..after a motor achieve 80% running..it switch to Delta.It mean the motor running with full capacity ( 415 volt )..For more detail,please read some post about star delta starter below :-

http://www.electricneutron.com/electric-motor/star-delta-motor-connection/
http://www.electricneutron.com/motor-control/star-delta-starter/

welcome to the site
It is great to see new input from new members.
but
please check the original post date
this is from 2007 (5 years old);)
 

Similar Topics

Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
Replies
6
Views
2,612
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
Replies
5
Views
98
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
Replies
0
Views
51
I have some logic that I have written within a 5380 series controller that tracks the time an event is started, while the event is running an RTO...
Replies
2
Views
79
I have an HMI 2711R - T4T Series B, and I want to know which PLCs, besides Micro 820, can communicate with it.
Replies
2
Views
80
Back
Top Bottom