Failed to set an IP using BootP

prinejr

Member
Join Date
Mar 2012
Location
Bakersfield, CA
Posts
1
Not the first time I've done this and never had this happen before.
I run BootP, can see the MAC address of the 1756-ENBT, select it and enter the IP address. I get the following message on the ENBT card: "IP address/mask/gateway config invalid". I'm using BootP version 2.3 and my ENBT is running firmware 6.002. Any suggestions?
Must have been the jet lag. I figured it out. Thanks
 
Last edited:
Have you done checking your network settings on the BootP.. The gateway, and subnet mask must be same as the network your PC and the 1756-ENBT connected to. If not, then change it.
 
I experienced the same...heres what fixed it...

In BOOT/TP go to Tools > Network Settings...Make sure your Gateway and Subnet Mask makes sense...My Gateway was not set to all zeros...Once i corrected ReRan the BOOT/TP...All is good...
 

Similar Topics

I am using a panelview plus and I am using the PLC system clock to sync the panelview time. For some reason I keep getting a panelview error as...
Replies
3
Views
4,874
and then when i open the windowmaker, intouch is shutdown... that's not work that's demo I have 30days demo
Replies
3
Views
105
I'm getting the Dreaded "Failed to go Online with the Controller, Unable to Open Connection - All Connections may be in use" I suspect an...
Replies
7
Views
424
I'm getting the Dreaded "Failed to go Online with the Controller, Unable to Open Connection - All Connections may be in use" I suspect an...
Replies
1
Views
177
I am trying to import addresses and symbols from a PanelBuilder32 application into the RSLogix 5 Address/Symbol database - however each time I...
Replies
5
Views
483
Back
Top Bottom