Leadfoot, we have been talking about the branch-circuit short-circuit ground-fault protection. This is not the same as the overload protection.
But, I did find in the NEC 430.6(C) For motors used with VFDs, the ampacity of conductors, switches, branch-circuit short-circuit and ground-fault protection shall be based on the maximum operating current maked on the motor or control nameplate, or both.
I sure don't like being wrong. But it's worse giving the wrong information and not correcting yourself.
But, I did find in the NEC 430.6(C) For motors used with VFDs, the ampacity of conductors, switches, branch-circuit short-circuit and ground-fault protection shall be based on the maximum operating current maked on the motor or control nameplate, or both.
I sure don't like being wrong. But it's worse giving the wrong information and not correcting yourself.