I have a Modicon compact plc. I downloaded my program no problem but when I try to go into run mode I get a stopcode error 4000(hex).
Any ideas?
 
If you are using Modsoft to program, hit escape to quit the PLC status screen, and go to the PLC and I/O status under utility menu and hit ALT {h} this will bring up the plc stop codes.
 
A Modicon Stop Error Code of 4000 is indicative of a "Bad I/O traffic cop table". Check your traffic cop (I/O map is the same thing).
 
Thanks for your help. It helped out a great deal. I got in touch with Schneider and they said I needed a loadable of an analog card I am using. Up and running hopfully I can make the customer happy now. :)
 