SLC 5/03 and SLC 5/04

hhuong

Member
Join Date
Nov 2004
Posts
58
In SLC 5/03, RS-232 port (Ch0) and RS-45(Ch1) are NOT the same network. And, there is no direct data path between these two ports.

How about in SLC 5/04? Is there a direct data path between these two ports?
 
The ports on the SLC are always separate.

The SLC-5/04 and SLC-5/05 do have some limited "passthrough" capabilities. The CPU has to process every one of the messages, though, so the performance isn't good enough to be considered a "network bridge" like the Logix products.

You will have to read up in the User Manuals about the Status bits you have to set, and the Routing Table in the SLC-5/05.
 

Similar Topics

Hello All! I am writing today because I cannot figure this out for the life of me. Another site I am affiliated with keeps having their slc 5/03s...
Replies
10
Views
115
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
109
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
119
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
125
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
2
Views
110
Back
Top Bottom