Communication between ControlLogix and Click PLC

phuz

Member
Join Date
Jun 2008
Location
Mohnton, PA
Posts
1,044
This is for more of a personal project, but I am wondering if anyone has done communication between the Automation Direct Click PLC and a ControlLogix (or CompactLogix). The CompactLogix I am using is an L18, which can be configured for MODBUS TCP, and it looks like the Click PLC can also do Modbus TCP, so that appears to be one method. Preferably, I would do something with a generic module or MSG instruction to retrieve data but haven't found any references on it.
 
On the Click PLC you have only Modbus TCP on the Ethernet connection.
The serial ports will have Modbus RTU or ASCII communication. I would not recommend using straight ASCII for the communications.

Regards,
Garry
 
I thought I read somewhere that these new units are Ethernet/IP capable, so I was hoping I may be able to do some messaging. Modbus TCP is OK though.
 

Similar Topics

Hello All, Last day we are facing some issued. After checking we found that no data transfer between Melsec communication module (AJ71UC24) and...
Replies
1
Views
1,591
Is this even possible? I need to get a string from a controllogix L64 processor into a Productivity3000. I've tried SLC type writes and CIP data...
Replies
2
Views
1,707
Hello everyone, Currently I am working with a PLC/HMI Horner XL7e over Ethernet/IP communication with an AB ControlLogix, and suddenly the...
Replies
0
Views
1,747
Dear all, I want to establish communication between Micro820 and Controllogix. Can it be done using MsG instruction over Ethernet/IP? Thanks :)
Replies
0
Views
1,926
Hello all, May I know how to configure and establish communication between PanelView Plus 1500 with ControlLogix 1756-L71? Figure above showed...
Replies
2
Views
3,281
Back
Top Bottom