1794-ADN Flashing I/O LED
Hi guys,
We have a problem with a 1794-ADN module that is flashing its I/O Status indicator red. This will flash for awhile and then the Mod/Net will turn red, then it will turn green again (as if it were trying to reset) and then do it all over again. The original problem appears to be a bad output block in the group. We replaced it. What we've done so far: Replaced everything at this point. The ADN, the RTD block, the three output blocks, and the DC input block. And replaced the bases as well. Any ideas? Thanks!
__________________
Just because you can doesn't mean that you should... |
|
|
|
#2 |
|
Member
![]() Join Date: May 2007
Location: Melbourne
Posts: 201
|
Sounds like the ADN had 3 out put cards and 1 in put card attached to it.
When you replace the ADN you need to download the IO configuration to ADN. Then it knows what sort of modules are attached to the unit. If you have another ADN with the same IO configuration then you can replace it by just changing the Devicenet address. What is the fault code on the Devicenet Master? Last edited by Ranjith; July 19th, 2012 at 02:09 AM. Reason: No of output cards |
|
|
|
#3 | |
|
Lifetime Supporting Member
|
Quote:
In the end we changed out the entire stick of I/O using ones we got from an unused machine. That still didn't fix it, so we replaced the DeviceNet scanner as well. That finally got things up and running. Thanks, John
__________________
Just because you can doesn't mean that you should... |
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Siemens IM 151-1 6es7 151-1aa03-0ab0 flashing LED | Bob O | LIVE PLC Questions And Answers | 9 | July 23rd, 2011 08:08 AM |
| Siemens Equivalent to AB's 1794-AENT and 1794 Flex I/O | Rob S. | LIVE PLC Questions And Answers | 1 | October 5th, 2009 02:09 PM |
| 1794 Flex I/O separate power supply | russrmartin | LIVE PLC Questions And Answers | 1 | September 2nd, 2009 12:46 AM |
| 1794 Flex I/O Error: Mod Config Reject | Mfleming | LIVE PLC Questions And Answers | 4 | June 2nd, 2009 07:58 AM |
| CPU 5/03 flashing DH485 LED | BigMac | LIVE PLC Questions And Answers | 1 | December 11th, 2003 04:32 AM |