Hello to everybody. I have the follow problem on a multiprocessor machine that has an ethernet network. Sometimes the network stops to work and monitoring the staus of the ENBT/A cards, it shows the follow decimal number in the entry status tag from the GSV instruction: 20736
Someone does know the meaning of the bits in the entry status tag of the ENBT/A module? This should help me in the debugg.
Tanks
 
what is the firmware version of the card? There is an issue where the card will stop working for 20 min or so after 721 days. I think it is 721. I'd update to the latest firmware revision.
 
Thanks for the clarification. I couldn't remember off the top of my head. Maybe it was the ControlNet at 72 days. Too many numbers to remember.
 
The initial version was 4.3, but I changed all the ENBT/A with old one with firmware revision 3.9 that didn't have problem in a previous machine. Now I am using 3.6 fw revision, but I have still the problem
 

Similar Topics

I have several Avery scale units and they are configured as Generic Ethernet modules, and I am actually reading the data fine for the weight...
Replies
2
Views
418
So Rockwell PLCs have some generic ethernet module options available in the IO tree configuration. With the standard generic ethernet module, you...
Replies
3
Views
728
Hi All, We are planning Establish communication between Power Energy Meter (Schneider PM5320) with Rockwell PLC. I am unable to get the Assembly...
Replies
4
Views
748
hi guys! I need to communicate a device with my 1756-L8, im confused about the class, instance and attribute i should use to send ASCII commands...
Replies
2
Views
507
Looking to see if there is any sort of publication or details on if I can tie a 1794 AENT module to a 3rd party eth/ip scanner (happens to be opto...
Replies
2
Views
699
Back
Top Bottom