Powerflex 40 Comms Loss

Hello. I have a wierd one, or at least I think a wierd one. It all started about 3 weeks ago.....

I have a powerflex 40 with a 22-comm-d module. It is on a devicenet (obviously) network of 20 drives. It is node 16, near the middle of the network. It all the sudden started dropping out, which caused a running feedback fault on the PLC. What's strange is sometimes it will show a fault 81, sometimes it will not. When it doesn't actually trip the drive out, operator can ack the fault and then keep on running. When the drive actually trips on fault 81, then maint has to be called to reset the fault. The way our plc is set up, is pretty much as soon as we don't see a running feedback from the drive, then it triggers a plc/HMI fault for the fan it was controlling. There is a comms loss timeout setup in the drive as default for 5 secs. So my thinking was we were missing that running feedback bit for less than 5 secs. I've added a fault delay to the program, to allow them to run if the running feedback doesn't stay on for more than 5 secs.

So, the event happens completely at random. It can happen 2 hours between, and up to a week between faults. So, I started out by replacing the 22-comm-d, no go. I then disconnected the HIM module thats mounted on the front of the bucket. No go. Went ahead and replaced the HIM module as well as the base and cable. Still no go. I then replaced the drive. Nope. I replaced the dnet cables going to/from the next node. Upgraded firmware on DNET card as well as PLC firmware (needed it anyway). And....nope. Replaced the terminating resistors on the dnet network. Added the recommended grounding to the I/O common (as mentioned in rockwell technote) And still no better. This is the only drive on a network of 20 that is experiencing any issues.

Now I've added some historian points to try and catch this gremlin, but even that's a little funky. I can see the fault status on the trend, but I have a running feedback tag that never goes low when the fault happens. Thinking maybe a stale tag when this experiences issues. I've just recently added some of the status bits from the 1756-dnb (DeviceFailureRegister, DeviceIdleRegister, ActiveNodeRegister, ScannerStatus, ScrollingDeviceAddress, ScrollingDevicesStatus, DeviceStatus[16]. The last fault we experienced, where it actually tripped the drive on fault 81, my new historian data didn't show this node as experiencing any issues.

So that's where I'm at. All these possible fixes came from myself (drive, HIM, cables, resistors and firmware) and Rockwell tech support. I am now at a loss. It appears there is some type of interference that is still present. Next step from Rockwell is to add a motor choke on the output of the drive, which is currently on order.

Sorry for the long story, but I feel too much is better than too little. Let me know if anyone can be of some assistance
  Reply With Quote
Old July 10th, 2018, 12:27 PM   #2
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 700
Have repairs been performed on any other drives on the network prior to this fault showing? Perhaps the problem isn't wit this drive, but another drive on the network is causing issues with this drive.
  Reply With Quote
Old July 10th, 2018, 12:41 PM   #3
bjkallmeyer
Member
United States

bjkallmeyer is offline
 
Join Date: Jul 2018
Location: Erlanger
Posts: 5
there was one drive (node 20) that was experiencing a fault 81 in this same time frame. That was found to be that the remote him module connection was flaky, and the HIM module would not light up. I replaced the HIM module and base on that drive but resulted in same thing, so believe the DSI port on that one went bad. I unplugged the him cable going to this drive, until it can be replaced. Since unplugging that one, I hadn't had an issue with it. That's the only thing I'm aware of
  Reply With Quote
Old July 10th, 2018, 02:11 PM   #4
bjkallmeyer
Member
United States

bjkallmeyer is offline
 
Join Date: Jul 2018
Location: Erlanger
Posts: 5
there was one drive (node 20) that was experiencing a fault 81 in this same time frame. That was found to be that the remote him module connection was flaky, and the HIM module would not light up. I replaced the HIM module and base on that drive but resulted in same thing, so believe the DSI port on that one went bad. I unplugged the him cable going to this drive, until it can be replaced. Since unplugging that one, I hadn't had an issue with it. That's the only thing I'm aware of
  Reply With Quote
Old July 12th, 2018, 08:12 AM   #5
bjkallmeyer
Member
United States

bjkallmeyer is offline
 
Join Date: Jul 2018
Location: Erlanger
Posts: 5
sparkie, do you think it could somehow be related? It does seem odd that they were both experiencing issues in the same time frame. The drives are physically located several bucket spaces away from eachother. It shouldn't make sense, but I've seen some strange stuff over the years. At any rate, the one drive with flaky HIM connection does need replaced regardless. Just trying to find an explanation as pretty much everything surrounding the "original post drive" has been replaced. I know I can alter the "A105" setting to pretty much make it go away, but I would rather try and find the root cause.
  Reply With Quote
Old July 12th, 2018, 08:36 AM   #6
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,782
Is the devicenet cable possibly picking up noise? When I have seen this with bucket mounted drives on D-net, it usually affected multiple drives.

I have also seen problem crop up when there is a motor with insulation breaking down and the increased noise going to ground affects the drive to which the motor is grounded first.

At one time about 10 years ago we experienced an issue with a batch of bad ribbon cables between the d-net module and VFDs, but I think those were PowerFlex 70s and I think you have replaced all the similar parts in your case already.

Since you have exhausted many other causes, I think a megger test on the motor could at least rule out a motor insulation problem and if you have access to the tools and skills, that is what I might try next.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old July 12th, 2018, 08:51 AM   #7
bjkallmeyer
Member
United States

bjkallmeyer is offline
 
Join Date: Jul 2018
Location: Erlanger
Posts: 5
I'm waiting on an o-scope from another plant to maybe see if we do have some interference on the dnet side. But like you said, usually if you have noise on the dnet cables, then it effects multiple drives. Not just single one out. I have megged the motor as well, from the bucket to the motor and locally at the peckerhead and both passed with flying colors. Maintenance is scheduled to replace this motor as well, just to eliminate of one more piece.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PowerFlex 40 Comm loss icehube LIVE PLC Questions And Answers 0 April 17th, 2017 07:47 PM
Powerflex 40 drive suddnly stopping while running & there is no alarm on the display sahebanna LIVE PLC Questions And Answers 1 April 2nd, 2012 01:51 AM
Powerflex 40 and Dynamic Braking Resistors Tharon LIVE PLC Questions And Answers 3 February 11th, 2011 07:04 AM
Interfacing PanelView 300, Powerflex 40 and SLC503 Processor dabanani LIVE PLC Questions And Answers 11 October 16th, 2010 09:12 PM
PowerFlex 40 vs. 70 infineum LIVE PLC Questions And Answers 3 September 20th, 2006 09:35 PM


All times are GMT -5. The time now is 08:46 AM.


.