Cabling between VFD and motor

2rlp

Member
Join Date
Sep 2006
Location
Mumbai
Posts
136
Hi,


The distance between a Yaskawa VFD GA700, 45KW and the motor is 75 meters. I am using an output inductor between the VFD and the motor. I would like to know of the following options, which would be better to use


Option A: A 35sqmm 3 core cable,



or


Option B: 35 sqmm 3 separate flexible wires, laid in a conduit pipe


Thanks


Ron
 
Manual shows screened cable but no inductor - contact the drive tech support and ask for their recommendation, you dont want to have to do it again with 75m of cable.