Client SCADA Getting Struck

prakasha

Member
Join Date
Dec 2022
Location
Davangere, Karnataka, India
Posts
75
Hello Everyone,

We are Using Plant PAX Process library3.1 and when we working with PLC logix Modification or edit something in the Program, Client SCADA getting struck for few sec and restore back. this is not regular it happens often. what could be the issue.
 
You might be having a bottleneck with the amount of system overhead time slice for plant communication.

What PLC is it? I'm suspecting it's a L7 series processor or less. Check the system time slice setting, you can increase that from whatever you have to about 50-100% more without issues. Keep in mind, you trade off your scan times to achieve better communication.
 
So the data stops updating on the SCADA (PlantPax) but not the PLC?

I would consider looking at the IGS driver (or associated Networking) between the PLC and SCADA as well as the L75's networking diagnostics.
 

Similar Topics

Hi. I am thinking about how to provide a monitor in case I have a PC (for example for the HMI/SCADA) installed in the control cabinet. The PC...
Replies
16
Views
6,146
Hi all, I got involved recently in a oil and gas Pipeline project, we have 5 DCS at each tank farm and a SCADA to monitor the dispatch and...
Replies
4
Views
3,837
Hi All, I have National Instrument OPC Server and Citect scada as Client. The Problem is, when One Probe fails in the field then Citect Scada...
Replies
3
Views
7,185
Hey every body , I am using citectscada v6 and I use Citectscada Web Client and I have a problem that I want some body to help me with ,,, the...
Replies
16
Views
10,639
dear verybody What's software Scada Server?What's software Scada Client? because I have suggest from my customer but i know only a WinCC? help me...
Replies
3
Views
1,510
Back
Top Bottom