PanelView Plus 7 Perf - Not a valid device

I downloaded Firmware 12 (PVP6_700-1500_12.00-20200922), installed in the PC and ME Firmware Upgrade Wizard does not work eny more.

A message appears.

I tried to reinstall and the same happens


:confused:

FirmwareError.jpg
 
I had this issue for the first time while working in a new plant. Version 11, but an older PV Plus 1000.

All I had to do was turn off my wireless adapter. I've never seen this before, never had to turn off wireless, but it is mentioned kind of off-handedly in that KB article.

It's strange, but if you run into this, try that first. Everything else is harder.
 