Sorry for such a long message, but I need to provide a bit of background info by describing the equipment.
I have a series of machines which has several conveyors used to transport pallets through each machine in sequence There is one main control panel with all the I/O hard-wired to various j-boxes through Hoffman wiring trough. The conveyor movement is via a 1/2 HP motor on each individual conveyor section. The motor wiring is in a separate wiring trough from the I/O wiring.
Prox switches are 2 wire AC by big name manufacturer "X" and used to track pallets as they move on/off each conveyor section.
The prox switch wiring and motor wiring are separated very well. Leads may come within 4" or so of each other in the j-box, but they do not run parallel to each other. Each j-box had a ground bar where the motors and prox switches are all grounded. There is then a #14 wire connecting the ground bar back to the ground bar in the main panel.
Now for the issue. The prox switch(es) are unreliable and go into what I'll call a lockout condition (flashing green power light) when motors are jogged. I can create the lockout condition by manually pushing in the contactor with an insulated object. Only way to clear the lockout condition is to cycle power to the prox switch(es).
I have 3 other various prox switches by various other manufacturers (all different part numbers) that I have successfully tried with no issues. Unfortunately none are a viable solution as they are either too big diameter or too short of sensing range or wrong type of cable connector. (They were just extras I had laying around.) But the point is that all function as they should with no "lockout" conditions. I even took 15' of cable from one of the prox switches and stuffed it in the motor lead wiring trough with no adverse affects.
Today, I had the distributor and "X" factory rep in. For testing purposes, they had me disconnect a switch from the machine (so the body was not grounded) and then unhook the ground wire from the cordset. And then the switch works perfectly. They claim they have seen this before with this particular series of prox switch. My contention is that the other 3 part numbers from various manufacturers (one was actually the same brand, just a different part number) all work with no issues so I need them to take the unreliable switches back. So distributor and factory rep are currently looking for a suitable, reliable, readily-available replacement.
My question, has anybody else ever experienced anything like this? How did you fix it? I've tried separating the motor and prox switch grounds and running them individually back to the main control panel. Made no difference.
I have a series of machines which has several conveyors used to transport pallets through each machine in sequence There is one main control panel with all the I/O hard-wired to various j-boxes through Hoffman wiring trough. The conveyor movement is via a 1/2 HP motor on each individual conveyor section. The motor wiring is in a separate wiring trough from the I/O wiring.
Prox switches are 2 wire AC by big name manufacturer "X" and used to track pallets as they move on/off each conveyor section.
The prox switch wiring and motor wiring are separated very well. Leads may come within 4" or so of each other in the j-box, but they do not run parallel to each other. Each j-box had a ground bar where the motors and prox switches are all grounded. There is then a #14 wire connecting the ground bar back to the ground bar in the main panel.
Now for the issue. The prox switch(es) are unreliable and go into what I'll call a lockout condition (flashing green power light) when motors are jogged. I can create the lockout condition by manually pushing in the contactor with an insulated object. Only way to clear the lockout condition is to cycle power to the prox switch(es).
I have 3 other various prox switches by various other manufacturers (all different part numbers) that I have successfully tried with no issues. Unfortunately none are a viable solution as they are either too big diameter or too short of sensing range or wrong type of cable connector. (They were just extras I had laying around.) But the point is that all function as they should with no "lockout" conditions. I even took 15' of cable from one of the prox switches and stuffed it in the motor lead wiring trough with no adverse affects.
Today, I had the distributor and "X" factory rep in. For testing purposes, they had me disconnect a switch from the machine (so the body was not grounded) and then unhook the ground wire from the cordset. And then the switch works perfectly. They claim they have seen this before with this particular series of prox switch. My contention is that the other 3 part numbers from various manufacturers (one was actually the same brand, just a different part number) all work with no issues so I need them to take the unreliable switches back. So distributor and factory rep are currently looking for a suitable, reliable, readily-available replacement.
My question, has anybody else ever experienced anything like this? How did you fix it? I've tried separating the motor and prox switch grounds and running them individually back to the main control panel. Made no difference.