Powerflex 753, clearing fault from HIM

LMDAVE

Member
Join Date
Oct 2006
Location
New Orleans, LA
Posts
50
I would think this would be a straight-forward function from the HIM of the Powerflex 753, but I can not find how to clear a fault from the HIM. All I find in the manual is parameter for DI Clear Fault, on how to clear it from a digital input, but how can you reset it from the HIM?

I see reference to a diagnostic menu, but the only commands are:

ESC REF PARA TEXT
 
It depends on programming. The default is that hitting the Stop resets a fault, but if that doesn't work, then either someone has changed it, or the fault is one that cannot be reset.
 
Agreed; In general, you press the STOP button to clear a fault.

The "Stop Command = Fault Reset" has been part of A-B drive principles since at least the 1336 Plus family.
 
Thanks.

More than likely we have a bad drive. Have ground fault that wont reset, disconnected motor lead and cycled power. Still has same fault. Tech support told our tech that sounds like the drive is bad. So, that explains why we could reset the fault.
 

Similar Topics

How to remove faceplate from power flex 753 and not shutting the system down. What parameters should i change?
Replies
1
Views
102
Hi all, I am having a problem with a powerflex 753 we have on site and keep getting input phase loss. The drive has been running for a long...
Replies
7
Views
1,338
Hello Friends, We have a powerflex that stopped working sometime last week. It doesn't communicate over the network, or use CCW directly from my...
Replies
1
Views
439
Hello all! I am fairly new to the world of PLC's and this forum, so I apologize for my lack of knowledge. I have a Powerflex 753 that keeps...
Replies
6
Views
546
I am bench testing a PF753 (20f11nd096aa0nnnnn). I replaced the IGBT's and IC's in the firing circuit. Upon power up, I get the STS light...
Replies
7
Views
712