Intermittent Output
Prayder
Jun 2014
Arkansas
254
I have a 24VDC output wired up to a 24VDC Ice Cube relay. 24VDC + to pin 2 and 24VDC - to pin 7 of the relay. So when i toggle the outputs in the program they turn on and then off even though everything in the rung before the outputs stays on. They continually turn on/off in the program. On the physical card in the chassis the output stays lit up and doesnt drop out but I have no voltage on the outputs...
Any ideas?
Any ideas?
You have A relay connected. You are toggling outputS.
How many uses of this output address is in your program?? Most importantly, how many times is this address mapped to an output instruction?
You can post a screen shot of your logic for constructive criticism from others.
I realized the output was in 2 separate places and even though there was an AFI at the beginning of the second output rung... it was dropping out...
Thank you for pointing that out....
An AFI is an Always False Rung. It does not a don't scan and execute the rest of the rung and leave outputs the same command. It evaluates as false, and the rest of the logic gets executed. At times it would be nice if there was a don't scan the rest of the rung and change outputs command, but I'm sure it would get abused in ugly ways.
I generally create a dint and title it "always off" or "always on" and use the 32 bits for testing purposes, in case I ever need to toggle outputs on or off
Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
285
I had a comms fault between my VFD and Controller (5069-L320ERS2) that started about a month ago and happened maybe once a day to now where it...
272
Well, I'm working with this ABB plc project, and It's been a learning experience coming from Allen Bradley. The project can't be changed to an AB...
1,166
We have an application where we're communicating between a 1769-SDN a 3rd party device. For the most part things work fine. We're reading maybe...
2,739
HI all, i dont suppose anybody knows of some inverter range that might be specialized for running intermittently? we have a project where the...
1,421