WE have a ab 5/15 on a compressor when one of the techs hooked a hart475 to a discharge pressure tramsmitter , the compressor shut down on surge , it will only shut down if the surge limit is hit 3 times in a hour . So I log on to PLC and put a trend on the surge alarm as soon as he with on line with the transmitter the analog start spikeing up and down hitting the surge alarm, I check 3 more transmitter on this compressor and they all would screw with the analog every transmitter , each transmitter i tested was on diffent cards. And I two 475 same with both.
Has anyone ran in to this problem with AB 5/15 and hart 475
thanks
Billy
Has anyone ran in to this problem with AB 5/15 and hart 475