Hi all!
I’m working with Siemens S1200 PLC (CPU1214 C DC/DC/DC) and trying to setup a Muster –Slave PROFIBUS communication between Siemens S7-1200 PLC and GE PLC (GE Func). In my project I have a S7-1200 - PROFIBUS CM 1242-5 module as a DP Slave. I defined I/O transfer areas for this module and use DPRD_DAT and DPWR_DAT SFCs to send and receive data to a Master GE PLC.If I understood correctly this way i can transfer my Data Blocks.The problem is that i must also add to my hardware configuration a DP Master for my Slave CM 1242-5 module.I tried to import a GE Func PROFIBUS Master module GSD file(model IC693PBM200)into my project , but the error appears that it's not a GSD Slave file.Seems like I can import here only slave GSDs.
How can i overcome this problem?
Is there any program examples or tips for such a type of configurations?
Thanks in advance!
 
The easy way would be to exchange the IC693PBM200 for an IC693PBS201 or add the Slave module to the 90-30 PLC. Get GFK-2121 for how/if the PBM200 can act as a 'Slave'.
 

Similar Topics

Hi, I'm new to PLC programming and I have been playing around with the Siemens s1200 plc. I have been given a task to connect a gryphon d100...
Replies
6
Views
4,399
Hi guys, I'm a beginner in the PLC world and i would like some advices because i'm stuck in my program with the temperature controller. I work on...
Replies
3
Views
3,086
So I have finally had to bite the bullet and do some modifications to some Siemens PLC code written in TIA. I have got both V10.5 and V11...
Replies
3
Views
4,753
I have an S7 1212 with CM1242-5 Profibus module configured in TIA V13 to connect to an S7 315 2DP Profibus master. The configuration is set up for...
Replies
6
Views
2,590
My project uses, S71200 PLC, 2 analog input modules and a CM1242-5 Profibus DP slave. This system is standalone right now but becoming a part of...
Replies
0
Views
3,256
Back
Top Bottom