Hello All,

I am trying to connect an Allen Bradley PLC (1769-L16ER-BB1B Complactlogix) to a serial device using an HMS EN2SE-R Linking device.

This is my first time using a serial device, so I may be missing something obvious.

I configure the module in Studio 5000 and have followed all of the set up instructions in the HMS manual and the example video on the HMS website, however every time I try to download the configuration to the EN2SE-R, I get a box pop up that says "bad file name or number". It does the same thing when I try to save it.

I have attached a screen shot of the error.

Has anyone had this problem before?

Thanks!

HMS_EN2SE_R Error.jpg
 
Welcome to the PLCTalk forum community !

I found a post to the HMS forum from about 5 years ago suggesting that one cause for the "bad file name or number" message is that the *.ACD file is on a networked drive, which the embedded HMS utility can't handle.

Obviously the way to check that out is to put the *.ACD on your desktop or the C: drive somewhere.
 

Similar Topics

Hello all and happy Friday, I'm curious if anyone here has experience sending data over an Anybus Bolt II (HMS AWB6001-A) using a Compact Logix...
Replies
4
Views
769
Hi I have hms-en2mb-r module . When i configure and go online the module is faulted with error code 16#0009 and addition code 16#0001. Is there...
Replies
2
Views
730
I'm trying for the first time to use this HMS-EN2SE-R to communicate very tiny ASCII comms (3 characters max) From a Logix L71 to a very dumb...
Replies
0
Views
393
I have a Micrologix 1400 with an 1762-IR4 RTD. I use it to read airbag resistance on seats on an assembly line. I am often getting into a...
Replies
2
Views
1,199
Is it preferable to now install these with the EDS or as AB_Generic_Ethernet modules? We have six in total and the latest was setup successfully...
Replies
7
Views
2,441
Back
Top Bottom