FTView ME rev.12 dowloading issue
ceilingwalker
Mar 2010
Phoenix, AZ
1,586
Hello all, I am wanting to upload a new runtime file to my PV+ 1500 and it isn't allowing it because firmware appears to only accept those files created in rev.8 or earlier and I am using v.12. Is this the same as a CPU that requires a flash to a newer version or will this h-ware just not work with the newer s-ware? When I tried to use the transfer utility this is what it displayed:
When you create the runtime, you can choose to save it as an 8.0 application, see the attached image. This should run in your PV+1500. It should be easier than trying to flash your PanelView to V12, but to answer your question, it is the same as the PLCs in that the runtime file must match the version of the PanelView. Fortunately FactoryTalk View Studio, unlike Studio 5000 where you need multiple versions installed to match the various processors you work with, allows you to save mers in older formats.
Hi All, we've got abnormal experience when configuring Alarm Log Viewer on FTView SE Station Rev. 9.0. We configure columns starts with Date...
1,542
I am creating a global object in FTView SE 13. I want to have a string read from the PLC and display (in this case the tagname). So lets say...
167
I want to set user security level based on the value of a tag in my PLC called "ActiveUser". That tag will contain the A-P code which we use for...
207
Hi All, we've recently upgraded from FTView SE v10 to v12. Since the upgrade we've been having a problem where the HMI is slow to update tags in...
87
Hi, I have an issue accessing tags in 3 of my plcs'. When I go to select a tag there is no folder drop down as can be seen in the photo. Any...
86